Yes absolutely,   IAW: NFPA 25,  Standard for the Inspection, Testing, and 
Maintenance of Water-Based Fire Protection Systems, 2011 Edition

4.5.1    All components and systems shall be tested to verify that they 
function as intended. 

4.5.2    The frequency of tests shall be in accordance with this standard.

4.5.3    Fire protection system components shall be restored to full 
operational condition following testing, including reinstallation of plugs and 
caps for auxiliary drains and test valves.

4.5.4    During testing and maintenance, water supplies, including fire pumps, 
shall remain in service unless under constant attendance by qualified personnel 
or unless impairment procedures in Chapter 15 are followed.

4.5.5   Test results shall be compared with those of the original acceptance 
test (if available) and with the most recent test results.

4.5.6   When a major component or subsystem is rebuilt or replaced, the 
subsystem shall be tested in accordance with the original acceptance test 
required for that subsystem.



FRANK J. HERRICK
City Of Leawood Fire Department  
Office of the Fire Marshal
14801 Mission Road
Leawood, Ks. 66224-9560
Office:        913.681.6788 x 26 
Fax:            913.681.2399
Fire Sprinklers Save Lives, Property, the Environment, and Water - Protect what 
you value most!



-----Original Message-----
From: Ed Kramer [mailto:[email protected]] 
Sent: Thursday, March 31, 2011 11:46 AM
To: [email protected]
Subject: dry system trip test connection

I'm not NFPA 25 knowledgeable - hope someone can clue me in.

 

After the initial acceptance test, does the dry system trip test connection
ever get used again? 

 

Ed Kramer

Littleton, CO


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to