http://www.elkhartbrass.com/files/aa/downloads/catalog/catalog-f2-T.pdf
Towards the bottom of the file there is hose friction loss and some other
info
http://www.elkhartbrass.com/downloads/performance

I have a couple more around here...

Not sure if the FD is requiring you to prove end of hose pressures.  I have
only used a friction loss for the hose itself, or at least added it to the
required PSI at the hose valve i.e. 132 PSI minimum required instead of 100
PSI or in your case a loss for the footage.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Wednesday, April 06, 2011 1:10 PM
To: [email protected]
Subject: HW for hose

If you have to calculate a manual standpipe, what HW coefficient do you use
for standard fire hoses?

and what internal diameter is a 3" hose?

Thanks,
Greg

-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to