Usually, the friction loss in rubber-lined hose is LESS than friction loss
for steel pipe of same diameter,
even with hose couplings that restrict.  The calc with C=120 (used for steel
pipe) would then be
conservative on most rubber-lined hose applications.

scot deal
excelsior fire