Bryan, have you looked at all the options Not to use rack 
sprinklers,ESFR,CMSA...a lot of heads out there that would eliminate rack 
sprinklers.
--
Richard Carr, SET

---- Matt Grise <[email protected]> wrote: 
> Brian,
> 
> I have seen that it matters which has the higher pressure for exactly the 
> reason you are describing (when adding racks to an overhead system). If one 
> requires too high a pressure, it may overflow the other enough to blow the 
> calc.
> 
> I agree with the others though... if you can, just build the entire system 
> into one model and let the computer hash it out.
> 
> Matt Grisé PE*, LEED AP 
> Sales Engineer 
> Alliance Fire Protection 
> 130 w 9th Ave.
> North Kansas City, MO 64116
> 
> *Licensed in KS & MO 
> 
> 913.888.0647 ph 
> 913.888.0618 f 
> 913.927.0222 cell 
> www. AFPsprink.com 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Wednesday, April 20, 2011 9:25 AM
> To: [email protected]
> Subject: RE: Balancing Rack Calc's
> 
> Brian,
> 
> If this is a new system with roof & rack systems,then calc them as 1 
> system,adjust pipe size to give the required demand at each area and no 
> other balancing is needed.It's when you are adding a rack system to an 
> existing roof system riser that balancing is required.I was told by F.M. 
> years ago that if the 2 systems were within 1 PSI of each other,they 
> would not ask for a seperate balancing calc.Good luck.
> 
> Lamar Vaughn,SET
> 
> 
> On Wed, Apr 20, 2011 at 10:12 AM, Brian Harris wrote:
> 
> > Travis-
> > I'm using HydraCalc
> >
> > Brian Harris
> > FDFP Inc.
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Travis 
> > Mack,
> > SET
> > Sent: Wednesday, April 20, 2011 10:10 AM
> > To: [email protected]
> > Subject: Re: Balancing Rack Calc's
> >
> > What calc program are you using? Just put both the rack and overhead 
> > system
> > in the calc file and let the computer balance.
> > It has been over a decade since I did a 'separate' calc for each. 
> > Travis Mack, SET
> > MFP Design, LLC
> > www.mfpdesign.com
> >
> > Sent on the SprintR Now Network from my BlackBerryR
> >
> > -----Original Message-----
> > From: "Brian Harris" <[email protected]>
> > Sender: [email protected]: Wed, 20 Apr 2011
> > 10:06:42 To: <[email protected]>
> > Reply-To: [email protected]
> > Subject: Balancing Rack Calc's
> >
> > I knew sooner or later my luck would run out and I'd have a job with 
> > racks,
> > yes ladies and gentlemen this is the first time I've had to do an in 
> > rack
> > system. I've searched through code, searched past archives, and still 
> > am not
> > all warm and fuzzy with my conclusion, if someone would be so kind as 
> > to
> > either give me either an amen or send me to the corner with a dunce 
> > cap I
> > would greatly appreciate it.
> >
> >
> > I have done my overhead calc's, done my rack calc's, they are balanced 
> > to
> > within .5 psi of each other at a common point on the riser. My 
> > question is
> > this: does it matter which calc has the higher of the two pressures? 
> > The
> > reason I ask is when it comes to the combined calc and you balance the 
> > flow
> > at the common point on the riser I have tried two scenarios, if the 
> > higher
> > pressure is on the rack system and you plug in the "balance" formula I 
> > get
> > 981 gallons I need to add to the rack system which will work. If I 
> > tweak a
> > couple things and the overhead system is the higher pressure and plug 
> > that
> > into the "balance" formula I get 181 gallons that I need to add to the
> > overhead system and that will not work. What is the consensus of the 
> > forum?
> >
> >
> > Brian Harris
> >
> > First Defense Fire Protection
> >
> > 11957 Ramah Church Road
> >
> > Huntersville, NC 28078
> >
> > Phone: 704.948.3506
> >
> > Fax: 704.948.3507
> >
> > Nicet # 128476
> >
> >
> >
> >
> >
> >
> > =======
> > Email scanned by PC Tools - No viruses or spyware found.
> > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
> > http://www.pctools.com/
> > =======
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email 
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email 
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> >
> >
> > =======
> > Email scanned by PC Tools - No viruses or spyware found.
> > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
> > http://www.pctools.com/
> > =======
> >
> >
> >
> >
> >
> > =======
> > Email scanned by PC Tools - No viruses or spyware found.
> > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
> > http://www.pctools.com/
> > =======
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email 
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to