Brian,

I agree with everyone that the two systems should be calculated together as one when possible. But when you have an existing overhead system and the only information you have is base of riser demand, you can still enter this in your rack system hydraulic calculations for balancing purposes.

First, calculate an equivalent k-factor for the overhead system ( demand flow / sqrt(demand pressure) ). Then enter the existing overhead system as a sprinkler head in your rack system calculations using the overhead system's calculated equivalent k-factor. Use the overhead system's demand flow as your minimum required discharge.

Of course, NFPA 13 just allows equivalent k-factors for branch lines or "portions of systems" - not entire systems. But this will let you know if both systems will work simultaneously and you'll be able to see if your rack head pressures are being drug up by the overhead system or the other way around.

Trevor Spain
Igneus Incorporated


On 4/20/2011 9:32 AM, Matt Grise wrote:
Brian,

I have seen that it matters which has the higher pressure for exactly the 
reason you are describing (when adding racks to an overhead system). If one 
requires too high a pressure, it may overflow the other enough to blow the calc.

I agree with the others though... if you can, just build the entire system into 
one model and let the computer hash it out.

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS&  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, April 20, 2011 9:25 AM
To: [email protected]
Subject: RE: Balancing Rack Calc's

Brian,

If this is a new system with roof&  rack systems,then calc them as 1
system,adjust pipe size to give the required demand at each area and no
other balancing is needed.It's when you are adding a rack system to an
existing roof system riser that balancing is required.I was told by F.M.
years ago that if the 2 systems were within 1 PSI of each other,they
would not ask for a seperate balancing calc.Good luck.

Lamar Vaughn,SET


On Wed, Apr 20, 2011 at 10:12 AM, Brian Harris wrote:

Travis-
I'm using HydraCalc

Brian Harris
FDFP Inc.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis
Mack,
SET
Sent: Wednesday, April 20, 2011 10:10 AM
To: [email protected]
Subject: Re: Balancing Rack Calc's

What calc program are you using? Just put both the rack and overhead
system
in the calc file and let the computer balance.
It has been over a decade since I did a 'separate' calc for each.
Travis Mack, SET
MFP Design, LLC
www.mfpdesign.com

Sent on the SprintR Now Network from my BlackBerryR

-----Original Message-----
From: "Brian Harris"<[email protected]>
Sender: [email protected]: Wed, 20 Apr 2011
10:06:42 To:<[email protected]>
Reply-To: [email protected]
Subject: Balancing Rack Calc's

I knew sooner or later my luck would run out and I'd have a job with
racks,
yes ladies and gentlemen this is the first time I've had to do an in
rack
system. I've searched through code, searched past archives, and still
am not
all warm and fuzzy with my conclusion, if someone would be so kind as
to
either give me either an amen or send me to the corner with a dunce
cap I
would greatly appreciate it.


I have done my overhead calc's, done my rack calc's, they are balanced
to
within .5 psi of each other at a common point on the riser. My
question is
this: does it matter which calc has the higher of the two pressures?
The
reason I ask is when it comes to the combined calc and you balance the
flow
at the common point on the riser I have tried two scenarios, if the
higher
pressure is on the rack system and you plug in the "balance" formula I
get
981 gallons I need to add to the rack system which will work. If I
tweak a
couple things and the overhead system is the higher pressure and plug
that
into the "balance" formula I get 181 gallons that I need to add to the
overhead system and that will not work. What is the consensus of the
forum?


Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476






=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17320)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to