BAAAD Idea...So the GC says they will install the daft stops (or 8"/ - 1/3 of the depth as George states)....then they don't.
There is a fire 10 years from now and the Sprinkler Guy will spend a lot of money defending a BUILDING issue. At the least the listing should read similarly: "drafts tops shall be provided blah blah blah OR the remote area of XXXX sq ft shall be used" The we have a way around and give the owner / gc a choice. But by placing the requirement on a building feature, I will avoid using these heads as HARD AS I CAN. Greg On Tue, Jun 7, 2011 at 9:00 AM, George Church <[email protected]> wrote: > Like Marriott's requirement to use NFPA 13, not 13R? > Draft STOPs aren't required, can be curtains of plywood coming down 8" or > 1/3 the depth. Take a look at the Tyco catalog data on CC1 and CC2 > sprinklers- explains it all nicely. > > George L. Church, Jr., CET > Rowe Sprinkler Systems, Inc. > PO Box 407, Middleburg, PA 17842 > 877-324-ROWE 570-837-6335 fax > [email protected] > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Bill Brooks > Sent: Monday, June 06, 2011 1:52 PM > To: [email protected]; [email protected] > Subject: RE: CC1/CC2 or COIN sprinklers > > Do you have the 2009 IBC available? You're installing a 13R system? Would > sprinkler protection be necessary in the attic space? If NFPA 13R and no > sprinklers in the attic, then 3,000 sq ft draftstopping is needed. This > would definitely be the architect's job to show these in my opinion. If no > draftstopping is in the job, then your sprinkler scope extends to the attic. > If you must use a specially listed head for this purpose and if this head > requires 1000 sq ft draftstopping then it seems better to add the 3000 sq ft > draftstopping (or two units) and omit the sprinklers. > > Have I interpreted this correctly, aside from any Marriott special > requirements? > > Bill Brooks > > William N. Brooks, P.E. > Brooks Fire Protection Engineering Inc. > 372 Wilett Drive > Severna Park, MD 21146-1904 > 410-544-3620 > 410-544-3032 FAX > 412-400-6528 Cell > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Travis > Mack, SET > Sent: Monday, June 06, 2011 1:04 PM > To: [email protected] > Subject: Re: CC1/CC2 or COIN sprinklers > > Looking for some other forum experience here. How have you been dealing > with architects and GC's that state the IBC does not require draft stops in > an attic, so they are not willing to put them in when the CC heads are req'd > and the CC heads require a draft curtain to be installed? > > On 6/6/2011 9:23 AM, Matt Grise wrote: > > I agree. Just looked at that this morning. The handbook elaborates > > that > testing has found standard sprinks to be ineffective in short flat comb > concealed spaces. > > > > Matt Grisé PE*, LEED AP > > Sales Engineer > > Alliance Fire Protection > > 130 w 9th Ave. > > North Kansas City, MO 64116 > > > > *Licensed in KS& MO > > > > 913.888.0647 ph > > 913.888.0618 f > > 913.927.0222 cell > > www. AFPsprink.com > > > > > > -----Original Message----- > > From: [email protected] > [mailto:[email protected]] On Behalf Of Johnson, > Duane (NIH/OD/ORS) [C] > > Sent: Monday, June 06, 2011 11:22 AM > > To: '[email protected]'; '[email protected]' > > Subject: RE: CC1/CC2 or COIN sprinklers > > > > Yes. See 8.15.1.6 (2007). > > > > Duane Johnson, PE > > Program Manager > > Division of the Fire Marshal (Support Contractor) Office of Research > > Services National Institutes of Health > > 301-496-0487 > > > > "Protecting Science - One Sprinkler at a Time" > > > > > > -----Original Message----- > > From: Travis Mack, SET [mailto:[email protected]] > > Sent: Monday, June 06, 2011 12:08 PM > > To: [email protected] > > Subject: CC1/CC2 or COIN sprinklers > > > > Trying to settle a "discussion" here. When you have a flat concealed > > combustible space and<36" of clearance, are the specially listed heads > > required? > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)