yeah. These are not full draft stops by any means. It is just something that the architect misses on just about every job I have had these heads, and then the GC either has eat it, or get an extra from the owner to put in something the arch missed. It just leads to a battle. It is good when you have the option to let the GC know upfront that these are req'd, but that is not the case on every project.

On 6/7/2011 7:00 AM, George Church wrote:
Like Marriott's requirement to use NFPA 13, not 13R?
Draft STOPs aren't required, can be curtains of plywood coming down 8" or 1/3 
the depth. Take a look at the Tyco catalog data on CC1 and CC2 sprinklers- explains 
it all nicely.

George L. Church, Jr., CET Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bill Brooks
Sent: Monday, June 06, 2011 1:52 PM
To: [email protected]; [email protected]
Subject: RE: CC1/CC2 or COIN sprinklers

Do you have the 2009 IBC available?  You're installing a 13R system?  Would 
sprinkler protection be necessary in the attic space?  If NFPA 13R and no 
sprinklers in the attic, then 3,000 sq ft draftstopping is needed.  This would 
definitely be the architect's job to show these in my opinion.  If no 
draftstopping is in the job, then your sprinkler scope extends to the attic.
If you must use a specially listed head for this purpose and if this head 
requires 1000 sq ft draftstopping then it seems better to add the 3000 sq ft 
draftstopping (or two units) and omit the sprinklers.

Have I interpreted this correctly, aside from any Marriott special requirements?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack, SET
Sent: Monday, June 06, 2011 1:04 PM
To: [email protected]
Subject: Re: CC1/CC2 or COIN sprinklers

Looking for some other forum experience here.  How have you been dealing with 
architects and GC's that state the IBC does not require draft stops in an 
attic, so they are not willing to put them in when the CC heads are req'd and 
the CC heads require a draft curtain to be installed?

On 6/6/2011 9:23 AM, Matt Grise wrote:
I agree. Just looked at that this morning. The handbook elaborates
that
testing has found standard sprinks to be ineffective in short flat comb 
concealed spaces.
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS&   MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Monday, June 06, 2011 11:22 AM
To: '[email protected]'; '[email protected]'
Subject: RE: CC1/CC2 or COIN sprinklers

Yes.  See 8.15.1.6 (2007).

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Travis Mack, SET [mailto:[email protected]]
Sent: Monday, June 06, 2011 12:08 PM
To: [email protected]
Subject: CC1/CC2 or COIN sprinklers

Trying to settle a "discussion" here.  When you have a flat concealed
combustible space and<36" of clearance, are the specially listed heads
required?

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to