Just a side to this, and not a new rant! We have installed the required
"Draft Stopping" for coin/cc heads in the past and just bypassed the GC. We
co-ordinate with the Elect. Contractor so they run conduit and wire on the
bottom of the flat trusses, we draft stop the top using Dry wall, Plywood or
my personal favorite rolls of sheet metal flashing material. (Available in
various widths and ga.) A couple of MH and it’s a done deal. No it's not my
responsibility, no lost time polling forum, or peer groups. Job done move on
to the next project.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, June 07, 2011 9:08 AM
To: [email protected]
Subject: RE: CC1/CC2 or COIN sprinklers

Any different than the draft stops at the junction of ESFR and SSU's?
Prior precedent for building feature reqd by sprinkler listing criteria.
Draft curtain at vertical opening protected by water curtain?

There are others, so this isn't unique in requiring building features. We
note their need and our exclusion to providing them in our informative yet
entertaining proposal.

Window sprinklers- no horiz mullions without another set of WS below it- so
you COULD add another level of WS at every horizontal mullion and not change
building features. Architect /Owner might not like the appearance.

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, June 07, 2011 11:02 AM
To: [email protected]; [email protected]
Subject: Re: CC1/CC2 or COIN sprinklers

I am not talking about an option, in order to use the specially listed
sprinklers, there is a requirement to have the areas draft stopped per se.
So 13 requires the listed sprinklers, the listed sprinkler requires the
building to be altered so the sprinklers can be used.

If that is the new precedence, then we are treading on very dangerous
ground.

Greg

On Tue, Jun 7, 2011 at 9:55 AM, steve <[email protected]> wrote:


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to