Why not take a piece of paper, write down the length of the run, multiply it by 
the FL/ft, and use a calculator to multiply the two and get the friction loss?
Then correct for any dif in elevation by multiplying the dif x .433. 
It really isn't that hard and you really don't need a pc to run a simple supply 
calc.

Ok, maybe I should say you SHOULDn'T need a pc....


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ralphy Henderson
Sent: Tuesday, June 07, 2011 12:29 PM
To: [email protected]; [email protected]
Subject: RE: Pump, Tank, 1000 ft suction line.....

Bob, 

That's kind of what I was getting at. I'll probably just have to submit a 
separate calc showing the 150% pump rating through the pump to the tank to 
prove the losses are acceptable. Does anyone know if there is a way to do this 
in a single calc in hydracalc? I can put in an additional water 'source' but 
then would have to enter in a static, res, and flow for the tank to get it to 
run through the program and these numbers are unknown (except for static).

Thanks,

RB


--- On Mon, 6/6/11, Bob <[email protected]> wrote:

From: Bob <[email protected]>
Subject: RE: Pump, Tank, 1000 ft suction line.....
To: [email protected]
Date: Monday, June 6, 2011, 11:05 PM

Ralph,
Looking at this I'm coming up with 20.3 psi loss in 1000' of pipe not counting 
fittings and valves.
(4.52*1000.00^1.85)/(140^1.85*6.4^4.85) = .0203   .0203 * 1000 = 20.3. 6.4" is 
ID of 6" Tyton Joint Pipe DI.  Fittings and valves will increase your losses.  
At 1500 gpm you will have .43 psi / ft loss.  These numbers will vary depending 
on pipe type and ID. As far as how to do it;  I think I would simply run the 
numbers through the calculation back to the tank.  Or better yet, if there are 
hydrants fed off of the tank have a flow test performed and calc back to that 
point of connection.

Bob Knight, CET III
208-318-3057
www.firebyknight.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Monday, June 06, 2011 4:37 PM
To: [email protected]; [email protected]
Subject: Re: Pump, Tank, 1000 ft suction line.....

Ralph -

My rough calcs say about 16 psi loss at 100% flow and 34 psi loss at 150% flow.
Unless this is an elevated tank, or your source is uphill from the pump, this 
won't work.

At 06:32 PM 6/6/2011, you wrote:
>at 1000 gpm, you are going to lose about 2 psi per 100' of 6" 
>ductile iron pipe.  At 1500 gpm, you are going to lose about 5 psi / 
>100' of DI pipe.  You need to have enough elevation between the tank 
>and pump to provide a positive pressure at the suction flange.
>
>On 6/6/2011 3:28 PM, Ralphy Henderson wrote:
>>Hi All,
>>
>>Can someone explain to me how one would go about calculating a fire 
>>pump being fed solely from a water storage tank but with a 6" x
>>1,000 ft suction line? I've calculated fire pumps off of tanks that 
>>had a small 10 ft. suction lines directly off the tank but never one 
>>with this amount of underground line and I'm concerned about making 
>>sure friction losses in the suction are properly accounted for. The 
>>pump is 75 psi @ 1000 gpm.
>>
>>We use hydracalc, and typically when a fire pump and tank scenario 
>>comes up we have only one 'source', the pump, being specified.
>>Would this change in this instance? I guess the main thing I'm 
>>concerned about is coming up with a negative pressure at the suction 
>>flange due to such a long run.
>>
>>Any help?
>>
>>-RB
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>__________ Information from ESET NOD32 Antivirus, version of virus 
>signature database 6185 (20110606) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
>
>

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to