You need to flow 150% IF you have it available.
Many don't realize this, and require it when it is not a #20 requirement.

Just like an office building we looked at yesterday with a BCO. Doesn't need 
standpipes, IF it did it would be manual wet, and there's a horrible (plumber) 
installed fire pump to give it an automatic water supply. However, the FDC is 
about useless, cause the bypass has only a closed OS&Y on it, no check, so its 
closed or the pump would just pump in a loop. But with that valve closed, the 
FDC supply has to rotate the impeller of the pump to get to the FHVs. Naturally 
they had the sensing lines coming off a common point, and while the sensing 
lines are to come off between the discharge check and gate on either pump, the 
check is supposed to be on the pump side; these guy installed the gate, then 
the check- then the sensing line T.  

The ignorant leading the incompetent leds to a non-compliant installation that 
didn't even need to happen. Glad I don't own the building- it was $50 to $100k 
waste of money. Nice stainless cabinets, tho. Top ones don't have pressure 
gauges.....


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of IPA
Sent: Wednesday, June 08, 2011 7:12 PM
To: [email protected]
Subject: Re: Pump, Tank, 1000 ft suction line.....

George, what did you mean by "Don't think you'd have a need to provide positive 
suction head at 150%." Doesn't NFPA #20 5.14.3.2 require it to stay above 0 (or 
-3 for tanks) while flowing 150%?




On Tue, Jun 7, 2011 at 10:43 AM, George Church <[email protected]>wrote:

> It may- its been 10 years+ since they let me run HydraCAD back there.
> Did you call NH and ask em?
> One of the strengths they offer is someone who understands the program 
> answering your call.
> You could pretend the tank is a piece of UG and is the incoming 
> supply- set your flow test up to be 10,000 GPM at .5 PSI or 0 PSI Run 
> it thru the UG including the slop you need to get positive head 
> exceeding the friction loss in the supply piping Ignore the warning of 
> low suction- Check result for positive pressure to the fire pump at 
> system demand. Don't think you'd have a need to provide positive 
> suction head at 150%.
>
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ralphy 
> Henderson
> Sent: Tuesday, June 07, 2011 1:00 PM
> To: [email protected]
> Subject: RE: Pump, Tank, 1000 ft suction line.....
>
> No, I don't need a PC to do the calc but I'd like for hydra calc to 
> show all this w/o an additional set. Things like that tend to confuse 
> the AHJ's - especially hand written things. You would think a multi 
> thousand dollar program would be able to take the calc from a tank to 
> the pump and to the system in one report - but it looks like that's not the 
> case.
>
>
>
>
>
>
>
> --- On Tue, 6/7/11, George Church <[email protected]> wrote:
>
> From: George Church <[email protected]>
> Subject: RE: Pump, Tank, 1000 ft suction line.....
> To: "[email protected]" 
> <[email protected]>
> Date: Tuesday, June 7, 2011, 4:47 PM
>
> Why not take a piece of paper, write down the length of the run, 
> multiply it by the FL/ft, and use a calculator to multiply the two and 
> get the friction loss?
> Then correct for any dif in elevation by multiplying the dif x .433.
> It really isn't that hard and you really don't need a pc to run a 
> simple supply calc.
>
> Ok, maybe I should say you SHOULDn'T need a pc....
>
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ralphy 
> Henderson
> Sent: Tuesday, June 07, 2011 12:29 PM
> To: [email protected]; [email protected]
> Subject: RE: Pump, Tank, 1000 ft suction line.....
>
> Bob,
>
> That's kind of what I was getting at. I'll probably just have to 
> submit a separate calc showing the 150% pump rating through the pump 
> to the tank to prove the losses are acceptable. Does anyone know if 
> there is a way to do this in a single calc in hydracalc? I can put in 
> an additional water 'source' but then would have to enter in a static, 
> res, and flow for the tank to get it to run through the program and 
> these numbers are unknown (except for static).
>
> Thanks,
>
> RB
>
>
> --- On Mon, 6/6/11, Bob <[email protected]> wrote:
>
> From: Bob <[email protected]>
> Subject: RE: Pump, Tank, 1000 ft suction line.....
> To: [email protected]
> Date: Monday, June 6, 2011, 11:05 PM
>
> Ralph,
> Looking at this I'm coming up with 20.3 psi loss in 1000' of pipe not 
> counting fittings and valves.
> (4.52*1000.00^1.85)/(140^1.85*6.4^4.85) = .0203   .0203 * 1000 = 20.3. 6.4"
> is ID of 6" Tyton Joint Pipe DI.  Fittings and valves will increase 
> your losses.  At 1500 gpm you will have .43 psi / ft loss.  These 
> numbers will vary depending on pipe type and ID. As far as how to do 
> it;  I think I would simply run the numbers through the calculation 
> back to the tank.  Or better yet, if there are hydrants fed off of the 
> tank have a flow test performed and calc back to that point of connection.
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Vince 
> Sabolik
> Sent: Monday, June 06, 2011 4:37 PM
> To: [email protected]; [email protected]
> Subject: Re: Pump, Tank, 1000 ft suction line.....
>
> Ralph -
>
> My rough calcs say about 16 psi loss at 100% flow and 34 psi loss at 
> 150% flow.
> Unless this is an elevated tank, or your source is uphill from the 
> pump, this won't work.
>
> At 06:32 PM 6/6/2011, you wrote:
> >at 1000 gpm, you are going to lose about 2 psi per 100' of 6"
> >ductile iron pipe.  At 1500 gpm, you are going to lose about 5 psi / 
> >100' of DI pipe.  You need to have enough elevation between the tank 
> >and pump to provide a positive pressure at the suction flange.
> >
> >On 6/6/2011 3:28 PM, Ralphy Henderson wrote:
> >>Hi All,
> >>
> >>Can someone explain to me how one would go about calculating a fire 
> >>pump being fed solely from a water storage tank but with a 6" x
> >>1,000 ft suction line? I've calculated fire pumps off of tanks that 
> >>had a small 10 ft. suction lines directly off the tank but never one 
> >>with this amount of underground line and I'm concerned about making 
> >>sure friction losses in the suction are properly accounted for. The 
> >>pump is 75 psi @ 1000 gpm.
> >>
> >>We use hydracalc, and typically when a fire pump and tank scenario 
> >>comes up we have only one 'source', the pump, being specified.
> >>Would this change in this instance? I guess the main thing I'm 
> >>concerned about is coming up with a negative pressure at the suction 
> >>flange due to such a long run.
> >>
> >>Any help?
> >>
> >>-RB
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >>For Technical Assistance, send an email to: 
> >>[email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email
> >to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >__________ Information from ESET NOD32 Antivirus, version of virus 
> >signature database 6185 (20110606) __________
> >
> >The message was checked by ESET NOD32 Antivirus.
> >
> >http://www.eset.com
> >
> >
>
> Vince Sabolik
> Christi Fire Protection, Inc.
> 11351 Pearl Road
> Strongsville, Ohio 44136
>
> T 440 572-7730  F 440 572-7719  Email:
> <mailto:[email protected]>[email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to