At 32FPS a 2" sch 40 will discharge 335 gpm.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, August 02, 2011 3:02 PM
To: [email protected]
Subject: How much discharge from a 2" system drain

Plumbing engineer is asking how much flow could come from a 2" main drain at
the riser.  They are sizing floor sinks to capture the discharge.  No we're
not discharging it outside like usual.  This isn't a "usual" client.

System pressures from the pump are around 200psi static and 180 psi
residual.  That's a whole other issue.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to