Since you didn't tell us what your flow was at that 180Psi residual I'll just guess and say 1000. In theory you could get that 1000 Gpm out of a 2" smooth bore outlet with only 71 PSI pito. If your using a very short main drain to that new floor sink I wouldn't expect a lot of friction loss from the piping unless your fire pump is remote to the main drain and the pipe between the two will create a lot of loss. Typical floor drain/sink rates are determined by the drain MFG. but the one I'm looking at say's 8" will handle up to 760 Gpm. That 8" pipe size not grate size.
That's one reason we see most main drains piped to the outside. Once they realize the volume of water that gets released regularly into the room and the size sanitary (NOT STORM) drain that requires, they opt for more main drain pipe. ( I say sanitary, because it's not storm drain water if it's off the floor where it can get contaminated.) System pressures from the pump are around 200psi static and 180 psi residual. That's a whole other issue. Craig L. Prahl, CET _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)