Since you didn't tell us what your flow was at that 180Psi residual I'll
just guess and say 1000. In theory you could get that 1000 Gpm out of a 2"
smooth bore outlet with only 71 PSI pito. If your using a very short main
drain to that new floor sink I wouldn't expect a lot of friction loss from
the piping unless your fire pump is remote to the main drain and the pipe
between the two will create a lot of loss.
Typical floor drain/sink rates are determined by the drain MFG. but the one
I'm looking at say's 8" will handle up to 760 Gpm. That 8" pipe size not
grate size.

That's one reason we see most main drains piped to the outside. Once they
realize the volume of water that gets released regularly into the room and
the size  sanitary (NOT STORM) drain that requires, they opt for more main
drain pipe. ( I say sanitary, because it's not storm drain water if it's off
the floor where it can get contaminated.) 

System pressures from the pump are around 200psi static and 180 psi
residual.  That's a whole other issue.

Craig L. Prahl, CET   