2.0" discharge 

Assume pitot of 60 psi

Coefficient of .07

Discharge of 647 gpm

I think you need to run that 2" main drain to the outside, sprinkler test 
discharge I'll allow to be run in a janitors sink.  No way for this 2" main 
drain and not to a floor drain unless I verify that no flooding or property 
damage will occur. 

Captain Frank J. Herrick 
City Of Leawood Fire Department  
14801 Mission Road
Leawood, Ks. 66224-9560
Office:        913.681.6788 x 26 
Fax:            913.681.2399
Fire Sprinklers Save Lives, Property, the Environment, and Water - Protect what 
you value most!

  

-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Tuesday, August 02, 2011 2:02 PM
To: [email protected]
Subject: How much discharge from a 2" system drain

Plumbing engineer is asking how much flow could come from a 2" main drain at 
the riser.  They are sizing floor sinks to capture the discharge.  No we're not 
discharging it outside like usual.  This isn't a "usual" client.

System pressures from the pump are around 200psi static and 180 psi residual.  
That's a whole other issue.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to