2.0" discharge Assume pitot of 60 psi
Coefficient of .07 Discharge of 647 gpm I think you need to run that 2" main drain to the outside, sprinkler test discharge I'll allow to be run in a janitors sink. No way for this 2" main drain and not to a floor drain unless I verify that no flooding or property damage will occur. Captain Frank J. Herrick City Of Leawood Fire Department 14801 Mission Road Leawood, Ks. 66224-9560 Office: 913.681.6788 x 26 Fax: 913.681.2399 Fire Sprinklers Save Lives, Property, the Environment, and Water - Protect what you value most! -----Original Message----- From: [email protected] [mailto:[email protected]] Sent: Tuesday, August 02, 2011 2:02 PM To: [email protected] Subject: How much discharge from a 2" system drain Plumbing engineer is asking how much flow could come from a 2" main drain at the riser. They are sizing floor sinks to capture the discharge. No we're not discharging it outside like usual. This isn't a "usual" client. System pressures from the pump are around 200psi static and 180 psi residual. That's a whole other issue. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)