High rise with main drain discharge to a receiver on the floor above. The
receiver was the size of two double laundry trays with an 8" main drain.
Worked fine.

On Tue, Aug 2, 2011 at 5:00 PM, Thom <[email protected]> wrote:

> Since you didn't tell us what your flow was at that 180Psi residual I'll
> just guess and say 1000. In theory you could get that 1000 Gpm out of a 2"
> smooth bore outlet with only 71 PSI pito. If your using a very short main
> drain to that new floor sink I wouldn't expect a lot of friction loss from
> the piping unless your fire pump is remote to the main drain and the pipe
> between the two will create a lot of loss.
> Typical floor drain/sink rates are determined by the drain MFG. but the one
> I'm looking at say's 8" will handle up to 760 Gpm. That 8" pipe size not
> grate size.
>
> That's one reason we see most main drains piped to the outside. Once they
> realize the volume of water that gets released regularly into the room and
> the size  sanitary (NOT STORM) drain that requires, they opt for more main
> drain pipe. ( I say sanitary, because it's not storm drain water if it's
> off
> the floor where it can get contaminated.)
>
> System pressures from the pump are around 200psi static and 180 psi
> residual.  That's a whole other issue.
>
> Craig L. Prahl, CET
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to