This recommendation came from somewhere (ie insurance company). Find the source and start asking there.
At 11:39 AM 8/3/2011, you wrote: >We have an industrial project with a 3hr firewall separating two areas. On >one side of the fire wall has no protection at the roof per its industrial >rating and on the other side is a paint area protected as EH GroupII >(.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product >passes through from one side to the other. We are being asked to put >sprinklers on the non protected side of the opening supplied by a deluge >system. Apparently I am overlooking the requirements (spacing, density, >etc.); where would I find these requirements or would I simply use the >requirements of the protected side - .40/2500 spaced at max 12'-0? > > > >Thank you, > > > >Bobby Gillett > >Sr. Project Manager > >Key Fire Protection, Inc. > >(731) 424-0130 office (731) 424-9285 fax > >(731) 267-4853 cell > > <mailto:[email protected]> >[email protected] > > > > > > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)