I think this really depends on whether this is a single building or two
buildings (and particularly on separate properties). As you suggest the
presence of the opening negates there even being a three-hour wall, it just
happens to be constructed so that it could be. So if it's a single building
with a separation or two adjacent buildings on the same property basic code
requirements will be different. The building my classroom is in has one fire
area per floor. There are CMU walls separating classrooms and classrooms
from halls but they have doors with glass. The reason for the heavy walls is
noise abatement, so although they look like two-hour or better walls the
doors do not meet the criterion for such and they are just partions.

On Wed, Aug 3, 2011 at 9:17 AM, <[email protected]> wrote:

> It's questionable if an unprotected opening that big even meets code.
>
> A limited area sprinkler system around the opening meets what code?
>
> Can you prove that .40/2500 for a limited area adjacent to the opening
> provides separation equal to that of a 3hr fire wall?
>
> There's a reason that a fire wall is present.  It is a means of passive
> protection.  In your case there is no sprinkler protection on one side.  In
> the event of a fire it limits the spread. BUT it also acts as a separation
> if the sprinklers do not work on the sprinklered side.  Fire walls have a
> purpose.
>
> So, if it was me I'd tell whoever came up with the idea to just put some
> sprinklers on the non-sprinklered side and all will be just fine, NO, can't
> do that.
>
> There is nowhere within the NFPA Standards where a particular density is
> given that correlates to a specific passive fire rating.  Not saying if you
> found a cracker-jack FPE that they couldn't run some calculations and come
> up with some value but again, active fire protection has its purpose and
> passive fire protection has its purpose.  They are not interchangeable.
>
> This opening should be examined to see if it's even permissible under any
> circumstance according to code, then appropriate measures should be pursued
> to provide the proper means to maintain the integrity of the separation.
>
>
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Bobby Gillett
> Sent: Wednesday, August 03, 2011 11:39 AM
> To: [email protected]
> Subject: Unprotected Opening
>
> We have an industrial project with a 3hr firewall separating two areas. On
> one side of the fire wall has no protection at the roof per its industrial
> rating and on the other side is a paint area protected as EH GroupII
> (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product
> passes through from one side to the other. We are being asked to put
> sprinklers on the non protected side of the opening supplied by a deluge
> system. Apparently I am overlooking the requirements (spacing, density,
> etc.); where would I find these requirements or would I simply use the
> requirements of the protected side - .40/2500 spaced at max 12'-0?
>
>
>
> Thank you,
>
>
>
> Bobby Gillett
>
> Sr. Project Manager
>
> Key Fire Protection, Inc.
>
> (731) 424-0130 office  (731) 424-9285 fax
>
> (731) 267-4853 cell
>
>  <mailto:[email protected]>
> [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to