Ron, I'd agree with you if the areas were not physically separated by a rated fire wall. But since they are, I would not apply the 15ft rule.
In industrial sites where there are product conveyors passing through rated walls it is common for a physical break in the conveyor system at the wall with a rated fire door tied into a sensing and release system with electronic stop commands tied into the conveyor. Sensors are installed to determine the product is not in position to hinder fire door closures and bump the conveyor to clear the opening, smoke or heat detection is often employed on both sides of the opening to start this whole shut down process. This is all automatic and happens in seconds. There are some provisions within the FM data sheets specifically 1-23 where spray sprinklers are shown as a means to protect small openings. However, is says specifically SMALL openings and it doesn't give any criteria for the discharge being equal to a specific hour-rating. The majority of the text within 1-23 calls for listed door assemblies at rated openings. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Wednesday, August 03, 2011 12:00 PM To: [email protected] Subject: Re: Unprotected Opening I'd say you protect per the rule that requires the higher demand area extend fifteen feet into the lesser demand area. I'd suggest that this means fifteen feet straight through the opening and fifteen feet to either side. This is in 13 and you'll need to find it per your in use edition. That would be normal for two hazards in one building. You could also look under "Exposure Protection" which provides guidelines for buildings too close together with openings but this seems to me to apply only between properties, not within buildings themselves. Finally there are the "holes through the floor" layouts for things like escalators but I don't think that's applicable. On Wed, Aug 3, 2011 at 8:39 AM, Bobby Gillett < [email protected]> wrote: > We have an industrial project with a 3hr firewall separating two areas. On > one side of the fire wall has no protection at the roof per its industrial > rating and on the other side is a paint area protected as EH GroupII > (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product > passes through from one side to the other. We are being asked to put > sprinklers on the non protected side of the opening supplied by a deluge > system. Apparently I am overlooking the requirements (spacing, density, > etc.); where would I find these requirements or would I simply use the > requirements of the protected side - .40/2500 spaced at max 12'-0? > > > > Thank you, > > > > Bobby Gillett > > Sr. Project Manager > > Key Fire Protection, Inc. > > (731) 424-0130 office (731) 424-9285 fax > > (731) 267-4853 cell > > <mailto:[email protected]> > [email protected] > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)