It's questionable if an unprotected opening that big even meets code. A limited area sprinkler system around the opening meets what code?
Can you prove that .40/2500 for a limited area adjacent to the opening provides separation equal to that of a 3hr fire wall? There's a reason that a fire wall is present. It is a means of passive protection. In your case there is no sprinkler protection on one side. In the event of a fire it limits the spread. BUT it also acts as a separation if the sprinklers do not work on the sprinklered side. Fire walls have a purpose. So, if it was me I'd tell whoever came up with the idea to just put some sprinklers on the non-sprinklered side and all will be just fine, NO, can't do that. There is nowhere within the NFPA Standards where a particular density is given that correlates to a specific passive fire rating. Not saying if you found a cracker-jack FPE that they couldn't run some calculations and come up with some value but again, active fire protection has its purpose and passive fire protection has its purpose. They are not interchangeable. This opening should be examined to see if it's even permissible under any circumstance according to code, then appropriate measures should be pursued to provide the proper means to maintain the integrity of the separation. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Wednesday, August 03, 2011 11:39 AM To: [email protected] Subject: Unprotected Opening We have an industrial project with a 3hr firewall separating two areas. On one side of the fire wall has no protection at the roof per its industrial rating and on the other side is a paint area protected as EH GroupII (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product passes through from one side to the other. We are being asked to put sprinklers on the non protected side of the opening supplied by a deluge system. Apparently I am overlooking the requirements (spacing, density, etc.); where would I find these requirements or would I simply use the requirements of the protected side - .40/2500 spaced at max 12'-0? Thank you, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)