It's questionable if an unprotected opening that big even meets code.  

A limited area sprinkler system around the opening meets what code?

Can you prove that .40/2500 for a limited area adjacent to the opening provides 
separation equal to that of a 3hr fire wall?

There's a reason that a fire wall is present.  It is a means of passive 
protection.  In your case there is no sprinkler protection on one side.  In the 
event of a fire it limits the spread. BUT it also acts as a separation if the 
sprinklers do not work on the sprinklered side.  Fire walls have a purpose.  

So, if it was me I'd tell whoever came up with the idea to just put some 
sprinklers on the non-sprinklered side and all will be just fine, NO, can't do 
that.

There is nowhere within the NFPA Standards where a particular density is given 
that correlates to a specific passive fire rating.  Not saying if you found a 
cracker-jack FPE that they couldn't run some calculations and come up with some 
value but again, active fire protection has its purpose and passive fire 
protection has its purpose.  They are not interchangeable.  

This opening should be examined to see if it's even permissible under any 
circumstance according to code, then appropriate measures should be pursued to 
provide the proper means to maintain the integrity of the separation.



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, August 03, 2011 11:39 AM
To: [email protected]
Subject: Unprotected Opening

We have an industrial project with a 3hr firewall separating two areas. On
one side of the fire wall has no protection at the roof per its industrial
rating and on the other side is a paint area protected as EH GroupII
(.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product
passes through from one side to the other. We are being asked to put
sprinklers on the non protected side of the opening supplied by a deluge
system. Apparently I am overlooking the requirements (spacing, density,
etc.); where would I find these requirements or would I simply use the
requirements of the protected side - .40/2500 spaced at max 12'-0?

 

Thank you,

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to