It looks to me they want a deluge water curtain for the opening. I would use the guidelines for glazing protection, keeping in mind it is generally for two hour rating, whereas you may need for three hours. The problem I see is if one side is already sprinklered, you might have to add the new deluge water curtain to the design area of the existing ceiling system adjacent to the opening. That might be tough depending on your safety factors.
Tony -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: August 3, 2011 10:01 AM To: [email protected] Subject: Re: Unprotected Opening This recommendation came from somewhere (ie insurance company). Find the source and start asking there. At 11:39 AM 8/3/2011, you wrote: >We have an industrial project with a 3hr firewall separating two areas. >On one side of the fire wall has no protection at the roof per its >industrial rating and on the other side is a paint area protected as EH >GroupII (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) >where product passes through from one side to the other. We are being >asked to put sprinklers on the non protected side of the opening >supplied by a deluge system. Apparently I am overlooking the >requirements (spacing, density, etc.); where would I find these >requirements or would I simply use the requirements of the protected side - .40/2500 spaced at max 12'-0? > > > >Thank you, > > > >Bobby Gillett > >Sr. Project Manager > >Key Fire Protection, Inc. > >(731) 424-0130 office (731) 424-9285 fax > >(731) 267-4853 cell > > <mailto:[email protected]> >[email protected] > > > > > > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)