To all,

Please review the UL listing for sprinkler head guards, we have seen a few 
cases where the sprinkler contractor "bought the farm" because the sprinkler 
head guards were specified by the Architect but were not listed for the ECOH 
sprinkler heads. If my old brain can remember, I cannot think of any head guard 
that is listed for the ECOH sprinkler. I might need to be "educated". 

Have a fire safe day!

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Graham Wyatt
Sent: Monday, September 05, 2011 4:45 PM
To: [email protected]
Subject: ECOH wire guards


Hi all

We have used ECOH Viking heads and want to install guards to them
The Viking D1 wire guard data sheet specifically states it is not to be
used with this head

I wondered if anyone has had experience in using ECOH protection with
wire guards.

Regards
 
Graham Wyatt
 
Fire Protection Engineers ltd
Street Address: 57 Leith St, CBD, Dunedin
Postal Address: PO Box 5168, Moray Place, Dunedin
 
Ph (03) 4790799
Fx (03) 4790788
Email [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to