Best thing for a contractor to do in this case is NOT to just put on cages that 
"work", but to first check with the Mfr for a listed/Approved model; if none 
available, RFI Architect and ask for direction since specified item does not 
appear to be available.
It would be smart to check with more than one mfr unless Architect has 
specified a certain specific mfr.

Happy Birthday, Jim, it's a really small industry :) but certainly full of TOP 
Notch people. Expect surprises all day.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Tuesday, September 06, 2011 12:11 PM
To: [email protected]
Subject: RE: ECOH wire guards

To all,

Please review the UL listing for sprinkler head guards, we have seen a few 
cases where the sprinkler contractor "bought the farm" because the sprinkler 
head guards were specified by the Architect but were not listed for the ECOH 
sprinkler heads. If my old brain can remember, I cannot think of any head guard 
that is listed for the ECOH sprinkler. I might need to be "educated". 

Have a fire safe day!

Jim Davidson 
 
Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Graham Wyatt
Sent: Monday, September 05, 2011 4:45 PM
To: [email protected]
Subject: ECOH wire guards


Hi all

We have used ECOH Viking heads and want to install guards to them The Viking D1 
wire guard data sheet specifically states it is not to be used with this head

I wondered if anyone has had experience in using ECOH protection with wire 
guards.

Regards
 
Graham Wyatt
 
Fire Protection Engineers ltd
Street Address: 57 Leith St, CBD, Dunedin Postal Address: PO Box 5168, Moray 
Place, Dunedin
 
Ph (03) 4790799
Fx (03) 4790788
Email [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to