George,
Would that it were that simple. There is a district here in Southern California which requires recessed quick response sprinklers in all single family garages, and that such sprinklers be provided with sprinkler guards. Steve Leyton and I, along with a few others have used all the considerable histrionics we have at our disposal to ask that this policy be changed, particularly since listed guards for recessed sprinklers are not manufactured. The response from that district was that their concern was not for the listing of the materials, but rather for the accidental impact discharge as a result of "lousy installation by contractors." They initially (2004) required sprinkler guards on concealed sprinklers in garages as well, however that was rescinded when a new fire marshal took over.

As of fifteen minutes ago, the policy for recessed sprinkler guards is still in force.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 9/6/2011 9:57 AM, George Church wrote:
Best thing for a contractor to do in this case is NOT to just put on cages that 
"work", but to first check with the Mfr for a listed/Approved model; if none 
available, RFI Architect and ask for direction since specified item does not appear to be 
available.
It would be smart to check with more than one mfr unless Architect has 
specified a certain specific mfr.

Happy Birthday, Jim, it's a really small industry :) but certainly full of TOP 
Notch people. Expect surprises all day.


George L. Church, Jr., CET Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Tuesday, September 06, 2011 12:11 PM
To: [email protected]
Subject: RE: ECOH wire guards

To all,

Please review the UL listing for sprinkler head guards, we have seen a few cases where the 
sprinkler contractor "bought the farm" because the sprinkler head guards were specified 
by the Architect but were not listed for the ECOH sprinkler heads. If my old brain can remember, I 
cannot think of any head guard that is listed for the ECOH sprinkler. I might need to be 
"educated".

Have a fire safe day!

Jim Davidson
Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500   Fax:302-234-1781



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Graham Wyatt
Sent: Monday, September 05, 2011 4:45 PM
To: [email protected]
Subject: ECOH wire guards


Hi all

We have used ECOH Viking heads and want to install guards to them The Viking D1 
wire guard data sheet specifically states it is not to be used with this head

I wondered if anyone has had experience in using ECOH protection with wire 
guards.

Regards

Graham Wyatt

Fire Protection Engineers ltd
Street Address: 57 Leith St, CBD, Dunedin Postal Address: PO Box 5168, Moray 
Place, Dunedin

Ph (03) 4790799
Fx (03) 4790788
Email [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to