Don't forget the part about designing the sprinklers for ordinary
hazard.  At least that's gone by the wayside ...

SML

It HAS gone by the wayside, hasn't it?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
ParsleyConsulting
Sent: Tuesday, September 06, 2011 11:45 AM
To: [email protected]
Subject: Re: ECOH wire guards

George,
Would that it were that simple.  There is a district here in Southern 
California which requires recessed quick response sprinklers in all 
single family garages, and that such sprinklers be provided with 
sprinkler guards.  Steve Leyton and I, along with a few others have used

all the considerable histrionics we have at our disposal to ask that 
this policy be changed, particularly since listed guards for recessed 
sprinklers are not manufactured.  The response from that district was 
that their concern was not for the listing of the materials, but rather 
for the accidental impact discharge as a result of "lousy installation 
by contractors."   They initially (2004) required sprinkler guards on 
concealed sprinklers in garages as well, however that was rescinded when

a new fire marshal took over.

As of fifteen minutes ago, the policy for recessed sprinkler guards is 
still in force.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 9/6/2011 9:57 AM, George Church wrote:
> Best thing for a contractor to do in this case is NOT to just put on
cages that "work", but to first check with the Mfr for a listed/Approved
model; if none available, RFI Architect and ask for direction since
specified item does not appear to be available.
> It would be smart to check with more than one mfr unless Architect has
specified a certain specific mfr.
>
> Happy Birthday, Jim, it's a really small industry :) but certainly
full of TOP Notch people. Expect surprises all day.
>
>
> George L.  Church, Jr., CET  
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of Jim
Davidson
> Sent: Tuesday, September 06, 2011 12:11 PM
> To: [email protected]
> Subject: RE: ECOH wire guards
>
> To all,
>
> Please review the UL listing for sprinkler head guards, we have seen a
few cases where the sprinkler contractor "bought the farm" because the
sprinkler head guards were specified by the Architect but were not
listed for the ECOH sprinkler heads. If my old brain can remember, I
cannot think of any head guard that is listed for the ECOH sprinkler. I
might need to be "educated".
>
> Have a fire safe day!
>
> Jim Davidson
>   
> Davidson Associates
> Fire Protection * Medical Gas * Code Consulting
> 302-994-9500   Fax:302-234-1781
>
>
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of Graham
Wyatt
> Sent: Monday, September 05, 2011 4:45 PM
> To: [email protected]
> Subject: ECOH wire guards
>
>
> Hi all
>
> We have used ECOH Viking heads and want to install guards to them The
Viking D1 wire guard data sheet specifically states it is not to be used
with this head
>
> I wondered if anyone has had experience in using ECOH protection with
wire guards.
>
> Regards
>
> Graham Wyatt
>
> Fire Protection Engineers ltd
> Street Address: 57 Leith St, CBD, Dunedin Postal Address: PO Box 5168,
Moray Place, Dunedin
>
> Ph (03) 4790799
> Fx (03) 4790788
> Email [email protected]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to