Sorry,
I had the standards flipped in my original email.  I was trying to
confirm of I needed to use the flushing rates from NFPA 20 (11-1.2,
99ed)not 24 for the UG supply pipe when a fire pump is involved on a
project.
I have been running into opposition when trying to get the UG contractor
to flush per 20 and just wanted to make sure they needed to.  I have a
local consultant who works for many of the AHJ's that is requiring this.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of JSM Fire
Pro
Sent: Wednesday, November 16, 2011 7:54 PM
To: [email protected]
Subject: RE: fire pump suction piping - flushing

Holy slippery slope Jake Pauls - this is a good one.

NFPA 24 is indeed the applicable standard for the lead-in.  The scouring
velocity is 10 fps.  But, the water supply, absent a pump sucking on it,
may
not be capable of giving you 10 fps.   Flushing the lead-in before
connecting to the pump is prudent.  But, if you can't make 10 fps, a
boroscope inspection might be in order.  Bottom line, don't send
anything gravel or smaller through the impeller.

Be careful with the idea of "flow as much as you can".  If you are
flushing an 8" lead-in and you put an 8" x 2" flanged reducer on the end
to facilitate flushing and the results are below the scouring velocity,
you did NOT flow as much as you can.  Devices that restrict the flush
activity are not acceptable reasons for the inability to achieve
scouring velocity. 

J. Scott Mitchell, PE
NFPA disclaimer unnecessary     

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, November 16, 2011 6:08 AM
To: SprinklerFORUM
Subject: fire pump suction piping - flushing

Where exactly does the flushing requirements of NFPA 24 come to play for
the suction piping on a fire pump?

It appears that the suction piping, even for a combined lead in, has to
be flushed per NFPA 24 back to the point of connection to the city main.

Am I correct on this thinking?  This means 2350GPM for a 8in lead in
instead of 1560GPM per NFPA 20.  What happens if you can't get this flow
rate?  I don't see an exception, like in 24, to just flow as much as you
can.  

  

 

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-781-7900 (w)

262-781-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20111116/dd425575/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to