Here you go .....

Dear  Mr. Martinez,

The underground lead from the point of connection to the city main into the 
building is the piping NFPA 20 is referring too.  I have attached some 
commentary from the 2010 edition which I believe clarifies your question.

14.1.1 Flushing.
Stones, gravel, blocks of wood, bottles, work gloves, and other foreign objects 
have been
found in underground piping and piping taking suction from municipal or private 
water mains
or water storage tanks when flushing and/or flow testing procedures are 
performed. Also,
objects in underground piping that are quite remote from the fire pump 
installation and that
would otherwise remain stationary during low-flow conditions may sometimes be 
carried into
the pump during the high-volume flows required during the fire pump acceptance 
test. Because
many of these objects can cause damage to the fire pump, flushing of suction 
piping
prior to connection to the fire pump minimizes potential damage from foreign 
objects during
the fire pump acceptance flow tests. See Exhibit II.14.1 for sample objects 
removed from
underground pipe.
For booster pumps taking suction from underground mains, the flushing flow rate 
should
be at least equal to that in Table 14.1.1.1(a) or (b), or the maximum water 
demand, whichever
is greater. The flushing flow rates given in Table 14.1.1.1(a) or (b) are based 
on 15 ft/sec (4.6
m/sec) water flow velocity, which is the basis for the minimum suction inlet 
pipe sizes in
Tables 4.25(a) and (b). The minimum suction pipe inlet sizes in Tables 4.25(a) 
and (b) are the
same for pumps of several different capacities.
Experience has shown that the fl ow rates established in Tables 14.1.1.1(a) and 
(b) are of
sufficient velocity to clear the suction piping of debris. Additionally, most 
of these fl ow rates
exceed the 150 percent point of the pump ratings where these pipe sizes are the 
minimum
mandated in Tables 4.25(a) and (b). For instance, the largest pump allowed to 
use a minimum
5 in. (125 mm) suction pipe is one rated at 500 gpm (1893 L/min). The peak (150 
percent)
point for a 500 gpm (1893 L/min) pump is 750 gpm (2839 L/min). For 5 in. (125 
mm) suction
pipes, the fl ush rate is 920 gpm (3482 L/min). In another instance, the 
largest pump allowed
to use an 8 in. (200 mm) suction pipe is one rated at 1500 gpm (5678 L/min). 
The peak
(150 percent) point for a 1500 gpm (5678L/min) pump is 2250 gpm (8516 L/min). 
For 8 in.
(200 mm) suction pipes, the flush rate is 2350 gpm (8895 L/min).
For fi re pumps taking suction from a storage tank, reservoir, or wet pit, the 
following
should be determined prior to the pump acceptance flow test:
1. No obstructing materials are in the water main, tank, reservoir, or pit.
2. Any piping to the pump suction inlet is free from obstructing material.
Although field experience is such that oftentimes actual flushing is done 
without a measurement
of the flow rate, verification of the flow rate should be determined. The 
actual fl ow rate can
be determined using methods such as pitot readings or flowmeters described in 
NFPA 291, Recommended
Practice for Fire Flow Testing and Marking of Hydrants (see Part III of this 
handbook).
Flushing is normally accomplished at the maximum flow rate available from the 
water supply. In
some jurisdictions, restrictions may be on the minimum suction pressures 
allowed. In most cases,
the fl ow at 150 percent of the fi re pump rating should not result in 
unacceptable minimum residual
suction pressures and should serve as an appropriate flushing flow rate. Where 
this scenario is not
the case, actual flushing fl ow rates should at least be equal to the maximum 
water demand for the
fi re protection system. Also important to know is that the flushing rates 
required by NFPA 24,
Standard for the Installation of Private Fire Service Mains and Their 
Appurtenances, are based on
a velocity of 10 ft/sec (3.1 m/sec) and not the rates required by NFPA 20.
Regardless of the flushing methods used, the installing contractor should never 
connect
piping to the underground stub-up without obtaining a copy of the Contractor's 
Material and
Test Certificate for Underground Piping from the site utilities contractor or 
the underground
piping installing contractor. This certificate provides verification that the 
underground piping
has been flushed in accordance with NFPA 24 and that no debris was present in 
the piping
system at the time of the test.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, November 18, 2011 10:04 AM
To: [email protected]
Subject: RE: fire pump suction piping - flushing

Did they cite a specific chapter and verse for that decision?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Friday, November 18, 2011 10:59 AM
To: [email protected]
Subject: RE: fire pump suction piping - flushing

Sent it NFPA20

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Justin
Reid
Sent: Friday, November 18, 2011 9:58 AM
To: [email protected]
Subject: Re: fire pump suction piping - flushing

Just curious... did you talk to the NFPA 20 rep? or the NFPA 24 rep?

Justin Reid

On Fri, Nov 18, 2011 at 10:00 AM, Dewayne Martinez
<[email protected]>wrote:

> NFPA confirmed that the UG is to be flushed per NFPA 20.
> Thanks,
> Dewayne
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of George Church
> Sent: Friday, November 18, 2011 8:33 AM
> To: [email protected]
> Subject: RE: fire pump suction piping - flushing
>
> AFSA members can get an informal interpretation for free by contacting

> tech services in Dallas- Tom W, Phil B, or Roland usually respond 
> pretty quickly.
>
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ed Kramer
> Sent: Thursday, November 17, 2011 11:55 AM
> To: [email protected]
> Subject: RE: fire pump suction piping - flushing
>
> You may have to seek an interpretation from NFPA.  I personally don't 
> think the requirements in 20 apply to the underground supply.
>
> Ed Kramer
> Littleton, CO
>
> > -----Original Message-----
> > From: [email protected] 
> > [mailto:sprinklerforum- [email protected]] On Behalf Of 
> > Dewayne Martinez
> > Sent: Thursday, November 17, 2011 9:34 AM
> > To: [email protected]
> > Subject: RE: fire pump suction piping - flushing
> >
> > Under 2-9.1 Suction pipe and fittings The suction components shall 
> > consist of all pipe, valves, and fittings from the pump suction 
> > flange to the connection to the public or private water service 
> > main, storage tank......
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Ed 
> > Kramer
> > Sent: Thursday, November 17, 2011 10:17 AM
> > To: [email protected]
> > Subject: RE: fire pump suction piping - flushing
> >
> > Dewayne,
> >
> > I'm going off memory, so you probably should verify this.  I believe

> > somewhere in NFPA 20 (the 'scope' section, maybe?), it says NFPA 20 
> > requirements begin at the suction control valve.  Assuming that's 
> > correct, any piping upstream of that is not subject to NFPA 20 
> > requirements.
> > Therefore the underground suction pipe need only be flushed per the 
> > requirements of NFPA 24, not 20.
> >
> > Your mileage may vary.
> > Ed Kramer
> > Littleton, CO
> >
> >
> >
> > > -----Original Message-----
> > > From: [email protected]
> > > [mailto:sprinklerforum-
> >
> > > [email protected]] On Behalf Of Dewayne Martinez
> > > Sent: Thursday, November 17, 2011 5:03 AM
> > > To: [email protected]
> > > Subject: RE: fire pump suction piping - flushing
> > >
> > > Sorry,
> > > I had the standards flipped in my original email.  I was trying to

> > > confirm of I needed to use the flushing rates from NFPA 20 
> > > (11-1.2, 99ed)not 24 for the UG supply pipe when a fire pump is 
> > > involved on a project.
> > > I have been running into opposition when trying to get the UG 
> > > contractor to flush per 20 and just wanted to make sure they 
> > > needed to.  I have a local consultant who works for many of the 
> > > AHJ's that is
> > requiring this.
> > > Dewayne Martinez
> > >
> > > Design Build Fire Protection
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111118/bebd4981/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to