Under 2-9.1 Suction pipe and fittings
The suction components shall consist of all pipe, valves, and fittings
from the pump suction flange to the connection to the public or private
water service main, storage tank......


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Thursday, November 17, 2011 10:17 AM
To: [email protected]
Subject: RE: fire pump suction piping - flushing

Dewayne, 

I'm going off memory, so you probably should verify this.  I believe
somewhere in NFPA 20 (the 'scope' section, maybe?), it says NFPA 20
requirements begin at the suction control valve.  Assuming that's
correct, any piping upstream of that is not subject to NFPA 20
requirements.
Therefore the underground suction pipe need only be flushed per the
requirements of NFPA 24, not 20.  

Your mileage may vary.
Ed Kramer
Littleton, CO



> -----Original Message-----
> From: [email protected] [mailto:sprinklerforum-

> [email protected]] On Behalf Of Dewayne Martinez
> Sent: Thursday, November 17, 2011 5:03 AM
> To: [email protected]
> Subject: RE: fire pump suction piping - flushing
> 
> Sorry,
> I had the standards flipped in my original email.  I was trying to 
> confirm of I needed to use the flushing rates from NFPA 20 (11-1.2, 
> 99ed)not 24 for the UG supply pipe when a fire pump is involved on a 
> project.
> I have been running into opposition when trying to get the UG 
> contractor to flush per 20 and just wanted to make sure they needed 
> to.  I have a local consultant who works for many of the AHJ's that is
requiring this.
> Dewayne Martinez
> 
> Design Build Fire Protection


_______________________________________________
Sprinklerforum mailing list
[email protected]