Dewayne, I'm going off memory, so you probably should verify this. I believe somewhere in NFPA 20 (the 'scope' section, maybe?), it says NFPA 20 requirements begin at the suction control valve. Assuming that's correct, any piping upstream of that is not subject to NFPA 20 requirements. Therefore the underground suction pipe need only be flushed per the requirements of NFPA 24, not 20.
Your mileage may vary. Ed Kramer Littleton, CO > -----Original Message----- > From: [email protected] [mailto:sprinklerforum- > [email protected]] On Behalf Of Dewayne Martinez > Sent: Thursday, November 17, 2011 5:03 AM > To: [email protected] > Subject: RE: fire pump suction piping - flushing > > Sorry, > I had the standards flipped in my original email. I was trying to > confirm of I needed to use the flushing rates from NFPA 20 (11-1.2, > 99ed)not 24 for the UG supply pipe when a fire pump is involved on a > project. > I have been running into opposition when trying to get the UG contractor > to flush per 20 and just wanted to make sure they needed to. I have a > local consultant who works for many of the AHJ's that is requiring this. > Dewayne Martinez > > Design Build Fire Protection _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum