Warning - stupid question in 3...2...1...

I just found myself in a strange argument about sprinkler spacing in a
box butler building Ord Group II storage to 12'0.  The bay spacing
between the butler framing uprights is inconsistent, but for
conversation sake I'll simplify the concept.

Take a bay to be 40'0, space 4 lines across for 10'0 between lines.
Take the next bay at 30'0 and throw 2 lines there with 15'0 between
lines.  (Reminder: I started this with "Warning, stupid question...")
For the 40'0 bay for 10'0 between lines the heads on the line are 12'0
for spacing of 120.  For the 30'0 bay the heads on the line are 8'0 for
spacing of 120.

Ok, with that really goofy situation set, here's the strange argument I
was in: When reviewing this design I rejected it based on the fact that
the heads spanning the beam between the bays are overspaced.  (5' + 7'6)
x 12' = 150sf / head.  Their argument was they were spacing to the bays
only.  I returned with 13-8.5.2.1 stating nothing about beams and
"bayspace" limiting the coverage at the deck.  Even had to say: Imagine
your standing on the floor under the beam at the roof deck, the floor
space that we're protecting doesn't care about the beam and looking up
at the four heads your S x L doesn't care about the beam either.

Maybe I'm just looking for clarification that I'm not completely insane.
I'm only halfway done my first coffee and I'm looking outside at snow
and had to scrape ice off my car this morning, so perhaps I'm having
issues today.  But this is one argument that I never thought I'd find
myself in the middle of.  To sum up a stupid question: For all intensive
purposes, can a butler framing beam (or any other deep beam for that
matter) at the roof essentially be a "wall" for determining your area
per sprinkler?

Mike Gallello
Confused?