Just thinking out loud...

It seems like the SxL method is more suited to regularly spaced heads. Would 
the square of coverage created by SxL really be centered on a sprinkler head, 
not putting the sprinkler head at the corner? So...if you draw the beam and the 
SxL squares centered on the sprinkler heads... If you take any square that is 
(5'+7.5') x 12' and place it so that it crosses the beam, it will overlap the 
SxL protection square of at least 3 sprinkler heads.

So it seems like there is no 150sf area that is intended to be protected by 
only 1 head. If a fire were to start in that area, would the intent of the 
design be to have 3 heads activate and cover the area with .2 gpm/ sf from 
overlapping spray patterns?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of C&H Fire - Mike 
Gallello
Sent: Wednesday, December 07, 2011 8:15 AM
To: [email protected]
Subject: Sprinkler spacing 101

Warning - stupid question in 3...2...1...

I just found myself in a strange argument about sprinkler spacing in a
box butler building Ord Group II storage to 12'0.  The bay spacing
between the butler framing uprights is inconsistent, but for
conversation sake I'll simplify the concept.

Take a bay to be 40'0, space 4 lines across for 10'0 between lines.
Take the next bay at 30'0 and throw 2 lines there with 15'0 between
lines.  (Reminder: I started this with "Warning, stupid question...")
For the 40'0 bay for 10'0 between lines the heads on the line are 12'0
for spacing of 120.  For the 30'0 bay the heads on the line are 8'0 for
spacing of 120.

Ok, with that really goofy situation set, here's the strange argument I
was in: When reviewing this design I rejected it based on the fact that
the heads spanning the beam between the bays are overspaced.  (5' + 7'6)
x 12' = 150sf / head.  Their argument was they were spacing to the bays
only.  I returned with 13-8.5.2.1 stating nothing about beams and
"bayspace" limiting the coverage at the deck.  Even had to say: Imagine
your standing on the floor under the beam at the roof deck, the floor
space that we're protecting doesn't care about the beam and looking up
at the four heads your S x L doesn't care about the beam either.

Maybe I'm just looking for clarification that I'm not completely insane.
I'm only halfway done my first coffee and I'm looking outside at snow
and had to scrape ice off my car this morning, so perhaps I'm having
issues today.  But this is one argument that I never thought I'd find
myself in the middle of.  To sum up a stupid question: For all intensive
purposes, can a butler framing beam (or any other deep beam for that
matter) at the roof essentially be a "wall" for determining your area
per sprinkler?

Mike Gallello
Confused?
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to