Just thinking out loud... It seems like the SxL method is more suited to regularly spaced heads. Would the square of coverage created by SxL really be centered on a sprinkler head, not putting the sprinkler head at the corner? So...if you draw the beam and the SxL squares centered on the sprinkler heads... If you take any square that is (5'+7.5') x 12' and place it so that it crosses the beam, it will overlap the SxL protection square of at least 3 sprinkler heads.
So it seems like there is no 150sf area that is intended to be protected by only 1 head. If a fire were to start in that area, would the intent of the design be to have 3 heads activate and cover the area with .2 gpm/ sf from overlapping spray patterns? Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of C&H Fire - Mike Gallello Sent: Wednesday, December 07, 2011 8:15 AM To: [email protected] Subject: Sprinkler spacing 101 Warning - stupid question in 3...2...1... I just found myself in a strange argument about sprinkler spacing in a box butler building Ord Group II storage to 12'0. The bay spacing between the butler framing uprights is inconsistent, but for conversation sake I'll simplify the concept. Take a bay to be 40'0, space 4 lines across for 10'0 between lines. Take the next bay at 30'0 and throw 2 lines there with 15'0 between lines. (Reminder: I started this with "Warning, stupid question...") For the 40'0 bay for 10'0 between lines the heads on the line are 12'0 for spacing of 120. For the 30'0 bay the heads on the line are 8'0 for spacing of 120. Ok, with that really goofy situation set, here's the strange argument I was in: When reviewing this design I rejected it based on the fact that the heads spanning the beam between the bays are overspaced. (5' + 7'6) x 12' = 150sf / head. Their argument was they were spacing to the bays only. I returned with 13-8.5.2.1 stating nothing about beams and "bayspace" limiting the coverage at the deck. Even had to say: Imagine your standing on the floor under the beam at the roof deck, the floor space that we're protecting doesn't care about the beam and looking up at the four heads your S x L doesn't care about the beam either. Maybe I'm just looking for clarification that I'm not completely insane. I'm only halfway done my first coffee and I'm looking outside at snow and had to scrape ice off my car this morning, so perhaps I'm having issues today. But this is one argument that I never thought I'd find myself in the middle of. To sum up a stupid question: For all intensive purposes, can a butler framing beam (or any other deep beam for that matter) at the roof essentially be a "wall" for determining your area per sprinkler? Mike Gallello Confused? _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum