I have seen it done more than once and tend to agree with the contractor.
 The beams are usually obstructions - especially close to the eaves where
they may be several feet deep.

Maybe an informal interp?

Greg

On Wed, Dec 7, 2011 at 8:42 AM, <[email protected]> wrote:

> The protection is adequate even if the beam isn't there. I don't believe
> NFPA says anything about averaging the distance from one head to another.
> If it did there could never be a standard coverage head in the same room as
> an extended coverage.
>
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Bobby Gillett
> Sent: Wednesday, December 07, 2011 7:36 AM
> To: [email protected]
> Subject: RE: Sprinkler spacing 101
>
> Ok I'll bite - If you draw out the protection on the floor at each bay I
> believe you will find proper coverage stopping at the bays due to the heads
> and lines being spaced accordingly. Even though the bay is not divide by a
> wall - each set of branchlines on each side should spray appropriately to
> the beam (bay divider at roof) - I suggest draw it out.
>
> Bobby Gillett
> Sr. Project Manager
> Key Fire Protection, Inc.
> (731) 424-0130 office  (731) 424-9285 fax
> (731) 267-4853 cell
> www.keyfireprotection.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
> Williams
> Sent: Wednesday, December 07, 2011 8:30 AM
> To: [email protected]
> Subject: Re: Sprinkler spacing 101
>
> I will jump in and say no, the beams cannot be treated as walls for
> spacing.
> The occupancy can be placed under the beams and go from one bay to the
> next,
> so the sprinkler spacing has to correspond.
>
>
> At 09:14 AM 12/7/2011, you wrote:
> >Warning - stupid question in 3...2...1...
> >
> >I just found myself in a strange argument about sprinkler spacing in a
> >box butler building Ord Group II storage to 12'0.  The bay spacing
> >between the butler framing uprights is inconsistent, but for
> >conversation sake I'll simplify the concept.
> >
> >Take a bay to be 40'0, space 4 lines across for 10'0 between lines.
> >Take the next bay at 30'0 and throw 2 lines there with 15'0 between
> >lines.  (Reminder: I started this with "Warning, stupid question...")
> >For the 40'0 bay for 10'0 between lines the heads on the line are 12'0
> >for spacing of 120.  For the 30'0 bay the heads on the line are 8'0 for
> >spacing of 120.
> >
> >Ok, with that really goofy situation set, here's the strange argument I
> >was in: When reviewing this design I rejected it based on the fact that
> >the heads spanning the beam between the bays are overspaced.  (5' + 7'6)
> >x 12' = 150sf / head.  Their argument was they were spacing to the bays
> >only.  I returned with 13-8.5.2.1 stating nothing about beams and
> >"bayspace" limiting the coverage at the deck.  Even had to say: Imagine
> >your standing on the floor under the beam at the roof deck, the floor
> >space that we're protecting doesn't care about the beam and looking up
> >at the four heads your S x L doesn't care about the beam either.
> >
> >Maybe I'm just looking for clarification that I'm not completely insane.
> >I'm only halfway done my first coffee and I'm looking outside at snow
> >and had to scrape ice off my car this morning, so perhaps I'm having
> >issues today.  But this is one argument that I never thought I'd find
> >myself in the middle of.  To sum up a stupid question: For all intensive
> >purposes, can a butler framing beam (or any other deep beam for that
> >matter) at the roof essentially be a "wall" for determining your area
> >per sprinkler?
> >
> >Mike Gallello
> >Confused?
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.1873 / Virus Database: 2102/4664 - Release Date: 12/06/11
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/996e1146/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to