that is what I am screaming..

On Wed, Dec 7, 2011 at 9:02 AM, Cliff Whitfield <[email protected]>wrote:

> But if your sprinkler can't spray under the beam because it is too deep,
> then you do your spacing off of the beam for proper coverage in that bay
> and
> then  make sure you have proper spacing for the next bay on the other side
> of the beam.  You are not going to get any water on the other side of the
> beam if the spray is blocked.
>
> Cliff Whitfield, SET
> President
> Fire Design, Inc.
> Ph: 337-261-8807
> Fx: 337-261-8808
>
>
>
> [email protected]
> www.fire-design.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
> Williams
> Sent: Wednesday, December 07, 2011 8:58 AM
> To: [email protected]
> Subject: RE: Sprinkler spacing 101
>
>
> >I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when
> determining the area of the sprinkler.
>
> Part (b) of that section states "Choose the larger of either twice the
> distance to the wall or obstruction of the distance to the next sprinkler"
>
> Twice the distance to the wall is 10', the distance between the sprinklers
> is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, as
> Mike stated.
>
> That was looking at it from the 12 x 10 side. If you look at it from the 8
> x
> 15 side, twice the distance is 15 ft and the distance between sprinklers is
> 13'-6. Therefore that side is OK, but the other is not.
>
> n'est pas?
>
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/c04bfc91/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to