OK, before the lynch mob heads for Stonington.... I understand the logic and it does make sense. It probably should be that way. However, if you space only around the beams and it is challenged (by an engineer, AHJ, attorney for the plaintiff, etc), there is no solid defence for it, based on this section of NFPA 13. Until the standard is changed, we have to work within it. How many times have we asked a question and also asked for the section to justify the answer?
At 10:18 AM 12/7/2011, you wrote: >OK - one bay you have 10' between branch lines with heads along branch lines >spaced proper per design hazard and are 5'-0 from the girder/beam/bay >divider (even if its not an obstruction) and on the other side you are 12' >between branch lines with heads along branch lines spaced proper per design >hazard and are 6'-0 from the girder/beam/bay divider - you still have proper >coverage in both bays and to the girder/beam/bay divider. > >Bobby Gillett >Sr. Project Manager >Key Fire Protection, Inc. >(731) 424-0130 office (731) 424-9285 fax >(731) 267-4853 cell >www.keyfireprotection.com > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Sprinkler >Academy - C Bilbo >Sent: Wednesday, December 07, 2011 9:14 AM >To: FORUM >Subject: RE: Sprinkler spacing 101 > > >This is one of those GREAT questions!! And it doesn't have a very good >answer.... > >In practice, spacing sprinklers to the beams is VERY common. I've done it >and I think anyone that has laid out a warehouse has done it. However, the >black and white text of the rules does say "twice the distance to the wall >or the distance to the next sprinkler, whichever is greater" (paraphrased >off the top of the head...) > >The technical committees have avoided this question because we didn't think >that there was a huge problem out there with it.... (VERY UNOFFICIAL >DISCUSSIONS and NOT the NFPA's official position!) > >I think it would be a great proposal for next cycle. And for the record, >when it comes up at the technical meeting, I will be speaking in favor of >the practice. > >It should be recognized that the above is my opinion as a member of the >NFPA, and has not been processed as a formal interpretation in accordance >with the NFPA Regulations Governing Committee Projects and should therefore >not be considered, nor relied upon, as the official position of the the >AFSA, NFSA, NFPA, nor any of their technical committees. > >Sincerely, > > >Cecil Bilbo >Academy of Fire Sprinkler Technology >Champaign, IL >217.607.0325 >www.sprinkleracademy.com >[email protected] > >OUR STUDENTS SAVE LIVES!! > > > > >> From: [email protected] >> To: [email protected] >> Subject: RE: Sprinkler spacing 101 >> Date: Wed, 7 Dec 2011 09:02:16 -0600 >> >> But if your sprinkler can't spray under the beam because it is too deep, >> then you do your spacing off of the beam for proper coverage in that bay >and >> then make sure you have proper spacing for the next bay on the other side >> of the beam. You are not going to get any water on the other side of the >> beam if the spray is blocked. >> >> Cliff Whitfield, SET >> President >> Fire Design, Inc. >> Ph: 337-261-8807 >> Fx: 337-261-8808 >> >> >> >> [email protected] >> www.fire-design.com >> >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected]] On Behalf Of Todd >Williams >> Sent: Wednesday, December 07, 2011 8:58 AM >> To: [email protected] >> Subject: RE: Sprinkler spacing 101 >> >> >> >I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when >> determining the area of the sprinkler. >> >> Part (b) of that section states "Choose the larger of either twice the >> distance to the wall or obstruction of the distance to the next sprinkler" >> >> Twice the distance to the wall is 10', the distance between the sprinklers >> is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, as >> Mike stated. >> >> That was looking at it from the 12 x 10 side. If you look at it from the 8 >x >> 15 side, twice the distance is 15 ft and the distance between sprinklers >is >> 13'-6. Therefore that side is OK, but the other is not. >> >> n'est pas? >> >> >> Todd G. Williams, PE >> Fire Protection Design/Consulting >> Stonington, CT >> 860.535.2080 >> www.fpdc.com >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >-------------- next part -------------- >An HTML attachment was scrubbed... >URL: ><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment >s/20111207/fe2dc4d4/attachment.html> >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >----- >No virus found in this message. >Checked by AVG - www.avg.com >Version: 2012.0.1873 / Virus Database: 2102/4665 - Release Date: 12/07/11 > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum