OK - one bay you have 10' between branch lines with heads along branch lines spaced proper per design hazard and are 5'-0 from the girder/beam/bay divider (even if its not an obstruction) and on the other side you are 12' between branch lines with heads along branch lines spaced proper per design hazard and are 6'-0 from the girder/beam/bay divider - you still have proper coverage in both bays and to the girder/beam/bay divider.
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Sprinkler Academy - C Bilbo Sent: Wednesday, December 07, 2011 9:14 AM To: FORUM Subject: RE: Sprinkler spacing 101 This is one of those GREAT questions!! And it doesn't have a very good answer.... In practice, spacing sprinklers to the beams is VERY common. I've done it and I think anyone that has laid out a warehouse has done it. However, the black and white text of the rules does say "twice the distance to the wall or the distance to the next sprinkler, whichever is greater" (paraphrased off the top of the head...) The technical committees have avoided this question because we didn't think that there was a huge problem out there with it.... (VERY UNOFFICIAL DISCUSSIONS and NOT the NFPA's official position!) I think it would be a great proposal for next cycle. And for the record, when it comes up at the technical meeting, I will be speaking in favor of the practice. It should be recognized that the above is my opinion as a member of the NFPA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the the AFSA, NFSA, NFPA, nor any of their technical committees. Sincerely, Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 217.607.0325 www.sprinkleracademy.com [email protected] OUR STUDENTS SAVE LIVES!! > From: [email protected] > To: [email protected] > Subject: RE: Sprinkler spacing 101 > Date: Wed, 7 Dec 2011 09:02:16 -0600 > > But if your sprinkler can't spray under the beam because it is too deep, > then you do your spacing off of the beam for proper coverage in that bay and > then make sure you have proper spacing for the next bay on the other side > of the beam. You are not going to get any water on the other side of the > beam if the spray is blocked. > > Cliff Whitfield, SET > President > Fire Design, Inc. > Ph: 337-261-8807 > Fx: 337-261-8808 > > > > [email protected] > www.fire-design.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Todd Williams > Sent: Wednesday, December 07, 2011 8:58 AM > To: [email protected] > Subject: RE: Sprinkler spacing 101 > > > >I think section 8.5.2.1.1-2 (NFPA 13 07ed) supports your thinking when > determining the area of the sprinkler. > > Part (b) of that section states "Choose the larger of either twice the > distance to the wall or obstruction of the distance to the next sprinkler" > > Twice the distance to the wall is 10', the distance between the sprinklers > is 12'-6". Per that section, L = 12'-6". S is 12', therefore SxL = 150, as > Mike stated. > > That was looking at it from the 12 x 10 side. If you look at it from the 8 x > 15 side, twice the distance is 15 ft and the distance between sprinklers is > 13'-6. Therefore that side is OK, but the other is not. > > n'est pas? > > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, CT > 860.535.2080 > www.fpdc.com > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20111207/fe2dc4d4/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.1873 / Virus Database: 2102/4665 - Release Date: 12/07/11 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum