Where in the IBC?  Ask him to provide that reference.  

There are some restrictions on insulation in concealed spaces but they are 
specific to the type of insulation, vapor barrier, flame spread, construction 
Type and Occupancy.  

I don't accept a response like that without a Code reference.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Seidl Jamie D.
Sent: Thursday, May 24, 2012 8:30 AM
To: Sprinkler Forum ([email protected])
Subject: IBC Question

I had an interesting comment from an architect yesterday on a project I am 
working on.
Wood frame building with 12" open web trusses.  Due to the floor/ceiling 
assembly rating, we won't have the minimum 12" to use concealed space 
sprinklers due to the batt insulation between the floors.  Accounting for the 
insulation, we have approximately 9" of clear space.  When the manufactures 
were contacted, they confirmed that this would be outside the listing of the 
concealed space sprinkler.  We suggested to the contractor that he fill the 
truss space with insulation per NFPA 13.  The RFI came back answered "The 
exception in NFPA for filling the concealed space with insulations ins 
technically not permitted by IBC and is not practically effective."
While I haven't begun to make the point that the sprinkler protection/spray 
pattern wouldn't be "practically effective" in this situation and violate the 
listings, is any one aware of the IBC not allowing the elimination of sprinkler 
protection in a combustible concealed space where the space is filled with 
insulation?
Thanks,
Jamie Seidl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120524/362544e1/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to