Ron,

That is indeed one of the difficulties encountered when dealing with AHJ's who lack the training and experience to interpret the adopted edition of the IBC correctly. The section you reference regarding the word "throughout" probably comes across my desk twice a month from clients on both sides of the table. It's become so common that I found a number for an ICC rep who could explain the concept, and simply stopped worrying about helping clarify the issue.

Here in California the code committee has adopted the 2009 edition of the I-codes, and modified them to address issues (real or imagined) that impact systems in this state. I don't have any serious heartburn with that, although I have disagreements with some of the revisions. My grip here is that the state code group has done a frighteningly awful job of getting the word out to AHJ's and the
people on the other side of the table as well.

California has mandated several changes to NFPA-13, and such changes are documented in a very
late chapter of the CBC and the CFC.  Among those changes are:

1 - no remote area reduction for quick response sprinklers in ordinary hazard occupancies

2 - reduced remote area for quick response sprinklers in light hazard occupancies must be flowing at least
seven sprinklers

3 - the pipe under a building or building foundation shall not contain mechanical joints. Whether this restriction applies to flanged joints or solvent weld joints has to date not been clarified.

Unless you had nothing better to do than troll through the code looking for such items, you'd never find it. The only reason I'm aware of this at all is that I submitted plans to an AHJ who sat on the committee which made these changes, and he directed my attention to the back of the book. There was also a suggestion of my either being an imbecile or a cyclops in the midst of a blinking spasm, but that's another story. Both conditions might be true, but
he was so angry I didn't wish to debate further.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 5/24/2012 6:51 AM, Ron Greenman wrote:
My pet peeve (amongst all my other pet peeves). If IBC is the adopted
building code in your state then it is no longer entitled IBC except
in casual conversation but is rather something else with a number
(probably Revised Code of Your State number XYZ),  and if the state or
local jurisdiction hasn't expunged Section [F] (2009 edition)
903.3.1.1 NFPA Sprinkler systems. "Where the provisions of this code
require that a building or portion thereof be equipped throughout with
an automatic sprinklers system in accordance with this section,
sprinklers shall be installed throughout in accordance with NFPA 13
except as provided in Section 903.3.1.1.1," or has explicitly had an
amendment stating what you were told then the law is the adopted
version of the former model IBC including everything it references. I
had the same problem with an AHJ that said 13 was only a standard and
because IBC only mentioned noncombustible materials in Chapter 7 and
not limited combustibles that IBC did not recognize the latter,
despite the paragraph quoted above that makes NFPA 13 a part of the
adopted law.

On Thu, May 24, 2012 at 6:32 AM,<[email protected]>  wrote:
Where in the IBC?  Ask him to provide that reference.

There are some restrictions on insulation in concealed spaces but they are 
specific to the type of insulation, vapor barrier, flame spread, construction 
Type and Occupancy.

I don't accept a response like that without a Code reference.

Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Seidl Jamie D.
Sent: Thursday, May 24, 2012 8:30 AM
To: Sprinkler Forum ([email protected])
Subject: IBC Question

I had an interesting comment from an architect yesterday on a project I am 
working on.
Wood frame building with 12" open web trusses.  Due to the floor/ceiling assembly rating, we won't 
have the minimum 12" to use concealed space sprinklers due to the batt insulation between the 
floors.  Accounting for the insulation, we have approximately 9" of clear space.  When the 
manufactures were contacted, they confirmed that this would be outside the listing of the concealed 
space sprinkler.  We suggested to the contractor that he fill the truss space with insulation per NFPA 
13.  The RFI came back answered "The exception in NFPA for filling the concealed space with 
insulations ins technically not permitted by IBC and is not practically effective."
While I haven't begun to make the point that the sprinkler protection/spray pattern 
wouldn't be "practically effective" in this situation and violate the listings, 
is any one aware of the IBC not allowing the elimination of sprinkler protection in a 
combustible concealed space where the space is filled with insulation?
Thanks,
Jamie Seidl
-------------- next part --------------
An HTML attachment was scrubbed...
URL:<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120524/362544e1/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to