To all:

Unless there was a recall on the sprinkler, this would be beyond the expertise 
of a typical sprinkler system inspector and tester.  The scope of 25 is to look 
at the system as installed and accepted by the AHJ.

This is a slippery slope.

Shane M. Clary, Ph.D.
Bay Alarm Company


Sent from my iPad

On Aug 2, 2012, at 10:35 AM, "Steve Leyton" <[email protected]> wrote:

> Do not agree.  They are, by definition 3.3.4.1, a CRITICAL DEFICIENCY.
> This trumps all that other stuff, IMHO.
> 
> SML
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
> Greenman
> Sent: Thursday, August 02, 2012 9:31 AM
> To: [email protected]
> Subject: Re: NFPA 25 inspection of sprinklers with heat collector plates
> installed
> 
> Can't do it for that reason Steve. If they were acceptable at
> installation then calling them out that way would be beyond the scope of
> NFPA 25 and the expertise of the technician. That is unless the tech is
> also a PE and is willing to make that call as part of the cost of an
> inspection. Of course if you don't point it out in some way and the
> place burns any half-assed lawyer can convince any jury that the tech,
> and by extension his employer, is incompetent, negligent, and liable.
> 
> On Thu, Aug 2, 2012 at 9:25 AM, Steve Leyton
> <[email protected]>wrote:
> 
>> Yes, because those plates have been shown to slow sprinkler response.
>> 
>> 
>> Steve Leyton
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Gregg 
>> Key
>> Sent: Thursday, August 02, 2012 9:23 AM
>> To: [email protected]
>> Subject: NFPA 25 inspection of sprinklers with heat collector plates 
>> installed
>> 
>> Forum, if you were inspecting a building and found some pendant 
>> sprinklers with the "heat collectors" installed, would you write it up
> 
>> as a deficiency and why?
>> 
>> Many moons ago they were accepted but later research proved they did 
>> not work.
>> 
>> C.Gregg Key, SET
>> Key Fire Protection Services,Inc
>> Project Manager
>> (O) 706-790-3473
>> (C) 706-220-8821
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ments/20120802/8c4ffd28/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to