To those who say this is outside of scope of NFPA-25 you are correct.  To those 
of you who want to call it a deficiency on your inspection report get a good 
lawyer because you are jeopardizing your business.  This is an engineering 
evaluation and outside scope of 25.  The appropriate way to handle is as an 
observation outside of NFPA-25 inspection with an appropriate disclaimer. We 
have appropriate language recommendations for our insured.



Top Myers
RelMark Group
961 Pottstown Pike
Chester Springs, PA 19425
610-321-2415 X-219   Cell 610-952-0965
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Thursday, August 02, 2012 1:30 PM
To: [email protected]
Subject: RE: NFPA 25 inspection of sprinklers with heat collector plates 
installed

Right but I think we all agree 25' spacing is a critical deficiency but NFPA 25 
doesn't tell us to look at spacing right?  So then we'd do as Ron suggests, OK 
the inspection and under separate cover tell the owner there is a suspected 
problem that should be evaluated.  It does tell us to look for things hanging 
off the heads so that gets included in the inspection.  Bottom line doing 
inspections IMHO is a high risk venture not really worth the current market 
rates.  You really can't do it right in this situation.  

Chris 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, August 02, 2012 12:01 PM
To: [email protected]
Subject: RE: NFPA 25 inspection of sprinklers with heat collector plates 
installed

If we are aware that this is a bad practice, and that it will impede or 
possibly prevent a sprinkler from operating when exposed to a fire in the 
immediate vicinity of its location, and do not report it as a deficiency, then 
"we" are gonna get our asses sued off.

A critical deficiency is one that "can have an effect o the performance of the 
fire protection system."  4.1.4.1 states, "The property owner or designated 
representative shall correct or repair deficiencies or impairments that are 
found during the inspection ..."  To this comment and Dr. Shane's (welcome to 
the Viper's Pit, BTW) I would say that this is NOT a theoretical and the 
question was posed by someone who IS trained and understood in the first place 
that this was an issue.  Don't take my word for it, ask your lawyer.

Steve Leyton




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Thursday, August 02, 2012 9:56 AM
To: [email protected]
Subject: RE: NFPA 25 inspection of sprinklers with heat collector plates 
installed

I'd flag it under NFPA 25 '10 - 5.2.1.  Plenty in there like foreign materials 
or in the wrong orientation (because the plate implies it's too far down from 
the actual ceiling and should be upright based on the BL location, OK, maybe 
that's weak).  You have no idea if it was AHJ approved condition before you got 
there.  If you do as Ron suggested I'd use 5.2.1 as you did a deficient 
inspection as that section tells you exactly what to look for at the sprinkler, 
there is foreign material hanging from part of the sprinkler.  Don't get me 
wrong I see where Ron is going for other things that are not mentioned like 
suspected small pipe size, incorrect density and incorrect spacing.  

Not sure I agree with Steve's using of the critical definition generically as a 
trump card for everything.  First, some other section must identify what you 
are looking for then you'd use the definitions to establish an impairment, 
critical or non-critical deficiency?  Is this a deficiency?  Yes under 5.2.1.  
Is it an impairment, no.  Is it a deficiency? Yes but I don't know which level 
as I don't have details. Short room you are probably in the jet and it won't 
make a difference.  Tall space you may be in the plume and might make a bigger 
difference.  In the end I'd never put my name on it as OK. 

What did you mean they were accepted?  Just because an ahj agreed doesn't mean 
they were ever acceptable by the code.  And many moons ago I'm sure there were 
plenty of AHJ that said no.  I seem to only have come across in places that 
have limited oversight.  I've seen them on system's installed in the last 5 
years. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, August 02, 2012 11:26 AM
To: [email protected]
Subject: Re: NFPA 25 inspection of sprinklers with heat collector plates 
installed

Gregg,

I'd make one of those "not part of the inspection" comments, but an area of 
potential concerne and do the "recommendation of an engineer's review."


On Thu, Aug 2, 2012 at 9:23 AM, Gregg Key <[email protected]> wrote:

> Forum, if you were inspecting a building and found some pendant 
> sprinklers with the "heat collectors" installed, would you write it up 
> as a deficiency and why?
>
> Many moons ago they were accepted but later research proved they did 
> not work.
>
> C.Gregg Key, SET
> Key Fire Protection Services,Inc
> Project Manager
> (O) 706-790-3473
> (C) 706-220-8821
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120802/ac39cc84/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to