Greg,
The TYCO BB1 might be a good fit.  They are spaced 6' O.C. and 16 - 22" down
from the peak.  This would require only one row of sprinklers and probably
not more than 1-1/2" piping.  Of course this depends on your water supply.
For your situation, if I understand it correctly, you will only need  a 9.6
psi start pressure.



Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Tuesday, August 07, 2012 3:35 PM
To: [email protected]
Subject: Re: attics and 12" deflector distance

I don't think the Attic sprinklers would work - the baffles might but you
would end up with 3 rows of heads in that small space.
Overkill for sure, The Tyco Attic heads would be very difficult to use I
think.

Thanks,
Greg

On Tue, Aug 7, 2012 at 4:30 PM, Travis Mack <[email protected]> wrote:

> Tyco attic sprinklers? Baffles?
>
> Travis Mack, SET
> MFP Design, LLC
>
> Sent from my iPhone
>
> On Aug 7, 2012, at 1:58 PM, Greg McGahan <[email protected]> wrote:
>
> > I don't know that anyone has a solutions, but I have a 6/12 attic 
> > over a Porte' Cochere that cannot possibly comply with 13 based on 
> > the minimum 5 ft from the eave requirement of 8.6.4.1.4.3 and the 
> > max deflector
> distance
> > of 12" from the member at the peak. if you measure the distance on 
> > the slope from the deflector to the eave where the joists meet per 
> > 13, it is 8'-3". Therefore there is no single way to comply fully. I 
> > am really just venting, but would welcome good ideas.
> >
> >
> > Thanks,
> > Greg
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > -------------- next part -------------- An HTML attachment was 
> > scrubbed...
> > URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hments/20120807/689a2cb2/attachment.html
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120807/6a2a05b9/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5183 - Release Date: 08/07/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to