Greg, The TYCO BB1 might be a good fit. They are spaced 6' O.C. and 16 - 22" down from the peak. This would require only one row of sprinklers and probably not more than 1-1/2" piping. Of course this depends on your water supply. For your situation, if I understand it correctly, you will only need a 9.6 psi start pressure.
Bob Knight, CET III 208-318-3057 www.firebyknight.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Tuesday, August 07, 2012 3:35 PM To: [email protected] Subject: Re: attics and 12" deflector distance I don't think the Attic sprinklers would work - the baffles might but you would end up with 3 rows of heads in that small space. Overkill for sure, The Tyco Attic heads would be very difficult to use I think. Thanks, Greg On Tue, Aug 7, 2012 at 4:30 PM, Travis Mack <[email protected]> wrote: > Tyco attic sprinklers? Baffles? > > Travis Mack, SET > MFP Design, LLC > > Sent from my iPhone > > On Aug 7, 2012, at 1:58 PM, Greg McGahan <[email protected]> wrote: > > > I don't know that anyone has a solutions, but I have a 6/12 attic > > over a Porte' Cochere that cannot possibly comply with 13 based on > > the minimum 5 ft from the eave requirement of 8.6.4.1.4.3 and the > > max deflector > distance > > of 12" from the member at the peak. if you measure the distance on > > the slope from the deflector to the eave where the joists meet per > > 13, it is 8'-3". Therefore there is no single way to comply fully. I > > am really just venting, but would welcome good ideas. > > > > > > Thanks, > > Greg > > > > -- > > Greg McGahan > > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > > 1160 McKenzie Road > > Cantonment, FL 32533 > > 850-937-1850 > > fax 850-937-1852 > > -------------- next part -------------- An HTML attachment was > > scrubbed... > > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac > hments/20120807/689a2cb2/attachment.html > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Greg McGahan Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20120807/6a2a05b9/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.2197 / Virus Database: 2437/5183 - Release Date: 08/07/12 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum