This thing sounds like it's about 14 by 28 total. Ought to be easy enough
to just flood the crap out of it. What about bumping up the density a
level, use QRs, and run a couple of lines with close spacing, like maybe
four heads per side? Get the AHJ to buy in. You'd almost have a hose going
on in the thing.


On Tue, Aug 7, 2012 at 4:32 PM, Travis Mack <[email protected]> wrote:

> Will the Tyco HIP sprinklers work at the ends?
>
> Travis Mack, SET
> MFP Design, LLC
>
> Sent from my iPhone
>
> On Aug 7, 2012, at 4:25 PM, Greg McGahan <[email protected]> wrote:
>
> > Hey Bob,
> >
> > If it had gabled ends they would work well. But the ridge is only about
> > 14'long and then there are hipped ends.
> >
> > On Tue, Aug 7, 2012 at 6:00 PM, Bob <[email protected]> wrote:
> >
> >> Greg,
> >> The TYCO BB1 might be a good fit.  They are spaced 6' O.C. and 16 - 22"
> >> down
> >> from the peak.  This would require only one row of sprinklers and
> probably
> >> not more than 1-1/2" piping.  Of course this depends on your water
> supply.
> >> For your situation, if I understand it correctly, you will only need  a
> 9.6
> >> psi start pressure.
> >>
> >>
> >>
> >> Bob Knight, CET III
> >> 208-318-3057
> >> www.firebyknight.com
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Greg
> >> McGahan
> >> Sent: Tuesday, August 07, 2012 3:35 PM
> >> To: [email protected]
> >> Subject: Re: attics and 12" deflector distance
> >>
> >> I don't think the Attic sprinklers would work - the baffles might but
> you
> >> would end up with 3 rows of heads in that small space.
> >> Overkill for sure, The Tyco Attic heads would be very difficult to use I
> >> think.
> >>
> >> Thanks,
> >> Greg
> >>
> >> On Tue, Aug 7, 2012 at 4:30 PM, Travis Mack <[email protected]>
> wrote:
> >>
> >>> Tyco attic sprinklers? Baffles?
> >>>
> >>> Travis Mack, SET
> >>> MFP Design, LLC
> >>>
> >>> Sent from my iPhone
> >>>
> >>> On Aug 7, 2012, at 1:58 PM, Greg McGahan <[email protected]>
> wrote:
> >>>
> >>>> I don't know that anyone has a solutions, but I have a 6/12 attic
> >>>> over a Porte' Cochere that cannot possibly comply with 13 based on
> >>>> the minimum 5 ft from the eave requirement of 8.6.4.1.4.3 and the
> >>>> max deflector
> >>> distance
> >>>> of 12" from the member at the peak. if you measure the distance on
> >>>> the slope from the deflector to the eave where the joists meet per
> >>>> 13, it is 8'-3". Therefore there is no single way to comply fully. I
> >>>> am really just venting, but would welcome good ideas.
> >>>>
> >>>>
> >>>> Thanks,
> >>>> Greg
> >>>>
> >>>> --
> >>>> Greg McGahan
> >>>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> >>>> 1160 McKenzie Road
> >>>> Cantonment, FL 32533
> >>>> 850-937-1850
> >>>> fax 850-937-1852
> >>>> -------------- next part -------------- An HTML attachment was
> >>>> scrubbed...
> >>>> URL: <
> >>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> >>> hments/20120807/689a2cb2/attachment.html
> >>>>
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>
> >>
> >>
> >> --
> >> Greg McGahan
> >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> >> 1160 McKenzie Road
> >> Cantonment, FL 32533
> >> 850-937-1850
> >> fax 850-937-1852
> >> -------------- next part --------------
> >> An HTML attachment was scrubbed...
> >> URL:
> >> <
> >>
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> >> s/20120807/6a2a05b9/attachment.html>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> -----
> >> No virus found in this message.
> >> Checked by AVG - www.avg.com
> >> Version: 2012.0.2197 / Virus Database: 2437/5183 - Release Date:
> 08/07/12
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >
> >
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120807/deacc5b8/attachment.html
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120807/7f3da554/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to