I've run into this situation many times where the geometry of the building doesn't allow you to comply with both the eave requirement and the 12" from the peak requirement w/o cold soldering. In most cases the AHJ's I've worked with felt compliance at the peak was more important than the eaves and I agree with that. These spaces are usually itsy bitsy with insulation filling almost everything at the eaves leaving you a little pocket to protect. With one AHJ we ended up complying with a row of sprinklers within 36" vertically of the peak as it would have been done in pre-2002 editions of '13. The TYCO Attic sprinklers sound good at first but when you're talking cramped little spaces like these the duct work usually makes complying with the listing of the attic sprinkler's obstruction criteria impossible. It's a balancing act but ultimately it's going to be a compromise that is called by the AHJ.
On Tue, Aug 7, 2012 at 4:32 PM, Travis Mack <[email protected]> wrote: > Will the Tyco HIP sprinklers work at the ends? > > Travis Mack, SET > MFP Design, LLC > > Sent from my iPhone > > On Aug 7, 2012, at 4:25 PM, Greg McGahan <[email protected]> wrote: > > > Hey Bob, > > > > If it had gabled ends they would work well. But the ridge is only about > > 14'long and then there are hipped ends. > > > > On Tue, Aug 7, 2012 at 6:00 PM, Bob <[email protected]> wrote: > > > >> Greg, > >> The TYCO BB1 might be a good fit. They are spaced 6' O.C. and 16 - 22" > >> down > >> from the peak. This would require only one row of sprinklers and > probably > >> not more than 1-1/2" piping. Of course this depends on your water > supply. > >> For your situation, if I understand it correctly, you will only need a > 9.6 > >> psi start pressure. > >> > >> > >> > >> Bob Knight, CET III > >> 208-318-3057 > >> www.firebyknight.com > >> > >> > >> > >> -----Original Message----- > >> From: [email protected] > >> [mailto:[email protected]] On Behalf Of Greg > >> McGahan > >> Sent: Tuesday, August 07, 2012 3:35 PM > >> To: [email protected] > >> Subject: Re: attics and 12" deflector distance > >> > >> I don't think the Attic sprinklers would work - the baffles might but > you > >> would end up with 3 rows of heads in that small space. > >> Overkill for sure, The Tyco Attic heads would be very difficult to use I > >> think. > >> > >> Thanks, > >> Greg > >> > >> On Tue, Aug 7, 2012 at 4:30 PM, Travis Mack <[email protected]> > wrote: > >> > >>> Tyco attic sprinklers? Baffles? > >>> > >>> Travis Mack, SET > >>> MFP Design, LLC > >>> > >>> Sent from my iPhone > >>> > >>> On Aug 7, 2012, at 1:58 PM, Greg McGahan <[email protected]> > wrote: > >>> > >>>> I don't know that anyone has a solutions, but I have a 6/12 attic > >>>> over a Porte' Cochere that cannot possibly comply with 13 based on > >>>> the minimum 5 ft from the eave requirement of 8.6.4.1.4.3 and the > >>>> max deflector > >>> distance > >>>> of 12" from the member at the peak. if you measure the distance on > >>>> the slope from the deflector to the eave where the joists meet per > >>>> 13, it is 8'-3". Therefore there is no single way to comply fully. I > >>>> am really just venting, but would welcome good ideas. > >>>> > >>>> > >>>> Thanks, > >>>> Greg > >>>> > >>>> -- > >>>> Greg McGahan > >>>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > >>>> 1160 McKenzie Road > >>>> Cantonment, FL 32533 > >>>> 850-937-1850 > >>>> fax 850-937-1852 > >>>> -------------- next part -------------- An HTML attachment was > >>>> scrubbed... > >>>> URL: < > >>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac > >>> hments/20120807/689a2cb2/attachment.html > >>>> > >>>> _______________________________________________ > >>>> Sprinklerforum mailing list > >>>> [email protected] > >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >>> _______________________________________________ > >>> Sprinklerforum mailing list > >>> [email protected] > >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >>> > >> > >> > >> > >> -- > >> Greg McGahan > >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > >> 1160 McKenzie Road > >> Cantonment, FL 32533 > >> 850-937-1850 > >> fax 850-937-1852 > >> -------------- next part -------------- > >> An HTML attachment was scrubbed... > >> URL: > >> < > >> > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > >> s/20120807/6a2a05b9/attachment.html> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >> ----- > >> No virus found in this message. > >> Checked by AVG - www.avg.com > >> Version: 2012.0.2197 / Virus Database: 2437/5183 - Release Date: > 08/07/12 > >> > >> _______________________________________________ > >> Sprinklerforum mailing list > >> [email protected] > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >> > > > > > > > > -- > > Greg McGahan > > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > > 1160 McKenzie Road > > Cantonment, FL 32533 > > 850-937-1850 > > fax 850-937-1852 > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120807/deacc5b8/attachment.html > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120807/93ebb84f/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum