Hey Bob,

If it had gabled ends they would work well. But the ridge is only about
14'long and then there are hipped ends.

On Tue, Aug 7, 2012 at 6:00 PM, Bob <[email protected]> wrote:

> Greg,
> The TYCO BB1 might be a good fit.  They are spaced 6' O.C. and 16 - 22"
> down
> from the peak.  This would require only one row of sprinklers and probably
> not more than 1-1/2" piping.  Of course this depends on your water supply.
> For your situation, if I understand it correctly, you will only need  a 9.6
> psi start pressure.
>
>
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg
> McGahan
> Sent: Tuesday, August 07, 2012 3:35 PM
> To: [email protected]
> Subject: Re: attics and 12" deflector distance
>
> I don't think the Attic sprinklers would work - the baffles might but you
> would end up with 3 rows of heads in that small space.
> Overkill for sure, The Tyco Attic heads would be very difficult to use I
> think.
>
> Thanks,
> Greg
>
> On Tue, Aug 7, 2012 at 4:30 PM, Travis Mack <[email protected]> wrote:
>
> > Tyco attic sprinklers? Baffles?
> >
> > Travis Mack, SET
> > MFP Design, LLC
> >
> > Sent from my iPhone
> >
> > On Aug 7, 2012, at 1:58 PM, Greg McGahan <[email protected]> wrote:
> >
> > > I don't know that anyone has a solutions, but I have a 6/12 attic
> > > over a Porte' Cochere that cannot possibly comply with 13 based on
> > > the minimum 5 ft from the eave requirement of 8.6.4.1.4.3 and the
> > > max deflector
> > distance
> > > of 12" from the member at the peak. if you measure the distance on
> > > the slope from the deflector to the eave where the joists meet per
> > > 13, it is 8'-3". Therefore there is no single way to comply fully. I
> > > am really just venting, but would welcome good ideas.
> > >
> > >
> > > Thanks,
> > > Greg
> > >
> > > --
> > > Greg McGahan
> > > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > > 1160 McKenzie Road
> > > Cantonment, FL 32533
> > > 850-937-1850
> > > fax 850-937-1852
> > > -------------- next part -------------- An HTML attachment was
> > > scrubbed...
> > > URL: <
> > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> > hments/20120807/689a2cb2/attachment.html
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20120807/6a2a05b9/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.2197 / Virus Database: 2437/5183 - Release Date: 08/07/12
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120807/deacc5b8/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to