There is no blanket requirement, NFPA 25 2010 4.16 covers what valves must be 
supervised, personally I think it's rather poorly worded, but if you read 
through the whole standard my impression is the intent of 4.16.2 Supervised 
Closed. The test outlet control valves shall be supervised closed. includes 
these valves, otherwise you could leave the meter bypass open and have no 
pressure.  Typically we'd lock a valve like this open.  One could argue that 
the test outlet control valve is defined as the test header control valve, but 
there's a checklist in the standard that makes mention that test header AND 
meter bypass valves need to be supervised (form S2.2).  
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com

________________________________

From: [email protected] on behalf of 
[email protected]
Sent: Fri 8/24/2012 1:06 PM
To: [email protected]
Subject: Supervised vales in pump room



Here is an easy one for Friday. Is there a general requirement that all valves 
in a pump room be supervised? I am wondering about the valves in a flow meter 
loop that are normally closed.

Ron Fletcher
Aero - Phoenix
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4502 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120824/ac3913a2/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to