In that case excuse two typos, that was from NFPA 20 2010, not 25. Clearly it's a Friday afternoon. Mike Morey, SET, CFPS Sprinkler Designer BMW Constructors, Inc. O: 317.651.0596 | C: 317.586.8111 www.bmwc.com
________________________________ From: [email protected] on behalf of [email protected] Sent: Fri 8/24/2012 1:35 PM To: [email protected] Subject: RE: Supervised vales in pump room I'm not sure NFPA #25 would apply to a new installation. NFPA 20 requires the pump enclosure to be supervised or controlled but I found nothing requiring valve supervision. I don't have access to the codes on line right now so I can't look it up without going old skool using a book and that's too much trouble for Friday. I think IFC requires supply valves to be supervised. Ron Fletcher Aero - Phoenix -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Morey, Mike Sent: Friday, August 24, 2012 10:21 AM To: [email protected] Subject: RE: Supervised vales in pump room There is no blanket requirement, NFPA 25 2010 4.16 covers what valves must be supervised, personally I think it's rather poorly worded, but if you read through the whole standard my impression is the intent of 4.16.2 Supervised Closed. The test outlet control valves shall be supervised closed. includes these valves, otherwise you could leave the meter bypass open and have no pressure. Typically we'd lock a valve like this open. One could argue that the test outlet control valve is defined as the test header control valve, but there's a checklist in the standard that makes mention that test header AND meter bypass valves need to be supervised (form S2.2). Mike Morey, SET, CFPS Sprinkler Designer BMW Constructors, Inc. O: 317.651.0596 | C: 317.586.8111 www.bmwc.com ________________________________ From: [email protected] on behalf of [email protected] Sent: Fri 8/24/2012 1:06 PM To: [email protected] Subject: Supervised vales in pump room Here is an easy one for Friday. Is there a general requirement that all valves in a pump room be supervised? I am wondering about the valves in a flow meter loop that are normally closed. Ron Fletcher Aero - Phoenix _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- A non-text attachment was scrubbed... Name: winmail.dat Type: application/ms-tnef Size: 4502 bytes Desc: not available URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120824/ac3913a2/attachment.bin> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- A non-text attachment was scrubbed... Name: winmail.dat Type: application/ms-tnef Size: 5698 bytes Desc: not available URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120824/ec58298f/attachment.bin> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
