If leaving the valve in the wrong position will impair the operation of the sprinkler system, then the valve must be supervised, see below.
NFPA 101 2012:9.7.2.1 Supervisory Signals. Where supervised automatic sprinkler systems are required by another section of this Code, supervisory attachments shall be installed and monitored for integrity in accordance with NFPA 72 , National Fire Alarm and Signaling Code, and a distinctive supervisory signal shall be provided to indicate a condition that would impair the satisfactory operation of the sprinkler system. Supervisory signals shall sound and shall be displayed either at a location within the protected building that is constantly attended by qualified personnel or at an approved, remotely located receiving facility. Also... IBC 2012:903.4 Sprinkler system supervision and alarms. All valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures and waterflow switches on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit. Exceptions: 1. Automatic sprinkler systems protecting one- and two-family dwellings. 2. Limited area systems serving fewer than 20 sprinklers. 3. Automatic sprinkler systems installed in accordance with NFPA 13R where a common supply main is used to supply both domestic water and the automatic sprinkler system, and a separate shutoff valve for the automatic sprinkler system is not provided. 4. Jockey pump control valves that are sealed or locked in the open position. 5. Control valves to commercial kitchen hoods, paint spray booths or dip tanks that are sealed or locked in the open position. 6. Valves controlling the fuel supply to fire pump engines that are sealed or locked in the open position. 7. Trim valves to pressure switches in dry, preaction and deluge sprinkler systems that are sealed or locked in the open position. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: [email protected] [mailto:[email protected]] Sent: Friday, August 24, 2012 1:36 PM To: [email protected] Subject: RE: Supervised vales in pump room I'm not sure NFPA #25 would apply to a new installation. NFPA 20 requires the pump enclosure to be supervised or controlled but I found nothing requiring valve supervision. I don't have access to the codes on line right now so I can't look it up without going old skool using a book and that's too much trouble for Friday. I think IFC requires supply valves to be supervised. Ron Fletcher Aero - Phoenix -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Morey, Mike Sent: Friday, August 24, 2012 10:21 AM To: [email protected] Subject: RE: Supervised vales in pump room There is no blanket requirement, NFPA 25 2010 4.16 covers what valves must be supervised, personally I think it's rather poorly worded, but if you read through the whole standard my impression is the intent of 4.16.2 Supervised Closed. The test outlet control valves shall be supervised closed. includes these valves, otherwise you could leave the meter bypass open and have no pressure. Typically we'd lock a valve like this open. One could argue that the test outlet control valve is defined as the test header control valve, but there's a checklist in the standard that makes mention that test header AND meter bypass valves need to be supervised (form S2.2). Mike Morey, SET, CFPS Sprinkler Designer BMW Constructors, Inc. O: 317.651.0596 | C: 317.586.8111 www.bmwc.com ________________________________ From: [email protected] on behalf of [email protected] Sent: Fri 8/24/2012 1:06 PM To: [email protected] Subject: Supervised vales in pump room Here is an easy one for Friday. Is there a general requirement that all valves in a pump room be supervised? I am wondering about the valves in a flow meter loop that are normally closed. Ron Fletcher Aero - Phoenix _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- A non-text attachment was scrubbed... Name: winmail.dat Type: application/ms-tnef Size: 4502 bytes Desc: not available URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120824/ac3913a2/attachment.bin> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum