The phrasing is to the effect "supply water to systems".  If it's normally 
closed it can't be a supply and wouldn't need supervision. Similar to jockey 
pump valve, they don't feed the systems during a fire. 

For example IFC 903.4 Sprinkler system supervision and alarms.
All valves controlling the water supply for automatic sprinkler systems, pumps, 
tanks, water levels and temperatures, critical air pressures and water-flow 
switches on all sprinkler systems shall be electrically supervised by a listed 
fire alarm control unit.