The phrasing is to the effect "supply water to systems". If it's normally closed it can't be a supply and wouldn't need supervision. Similar to jockey pump valve, they don't feed the systems during a fire.
For example IFC 903.4 Sprinkler system supervision and alarms. All valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures and water-flow switches on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit. Chris Cahill, PE* Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell 8201 Norman Center Drive Bloomington, MN 55437 Phone: 952.656.3652 Fax: 952.229.2923 [email protected] www.burnsmcd.com Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, August 24, 2012 12:06 PM To: [email protected] Subject: Supervised vales in pump room Here is an easy one for Friday. Is there a general requirement that all valves in a pump room be supervised? I am wondering about the valves in a flow meter loop that are normally closed. Ron Fletcher Aero - Phoenix _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum