Hard to take a swing at my friend and mentor here but anecdotal without
data to suggest this is a common problem worth addressing. Would the WFS
not been installed if the pipe ran outside the wall? If the mis-installed
connection came loose (there are thousands of flexible couplings out there
that have not let loose and every catastrophic coupling failure I've ever
seen--no more than half a dozen--have all been installation errors although
I suppose there is an occasional defective part) before opening and it was
outside the wall the damage would have been as severe. Everything is
entropic. All organized structures want to disorganize. That means
buildings want to fall down, parts want to break, installers want to cut
corners. What level of quality control do we need to lessen the effects of
entropy, and for how much? Prescriptive codes establish a minimum level
that we can't go below. We can certainly spend more to mitigate but it's
the owner's money, not ours, and we'd better be able to justify extras,
redundancies, higher quality of materials than those that just meet a
minimum, with real arguments that the man with the money can understand and
make informed decisions from. Not only didn't we harden every big building
in America after 9-11, but we didn't harden any buildings. Had 9-11 been
followed by an airplane hitting the Seats Tower, and then the Trans-america
Building, the Statue of Liberty, the Golden Gate Bridge, etc., then at some
point the reoccurrence of iconic American structures collapsing might have
sent us to a different assessment.

On Thu, Sep 13, 2012 at 6:48 PM, Ed Vining <[email protected]> wrote:

> We had a designer who insisted on having a waterflow indicator inside the
> building wall when this situation existed.  He even set it up with a longer
> retard than the system WFI's and a circuit that squashed the main WFI when
> a system WFI operated.  No sense confusing the FF's.  A flexible connection
> let go very early one morning, before the building was occupied.  The
> building owner was grateful for the WFI.
>
> Ed Vining, retired, guest.
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
> Cell 925-787-0465
>
>
> On Thu, Sep 13, 2012 at 4:57 PM, Jarron Gass <[email protected]>
> wrote:
>
> > My concern is probably shifting more to whether or not this should have a
> > flow switch for that portion of the piping.  I can accept that there is a
> > shutoff outside in the meter pit, but i feel like this should be
> monitored.
> >  That is probably more a want than a need.
> >
> > ~Jarron
> >
> > Sent from my Verizon Wireless Droid
> >
> >
> > -----Original message-----
> > From: [email protected]
> > To: sprinklerforum@firesprinkler.**org <[email protected]
> >
> > Sent: Thu, Sep 13, 2012 22:12:31 GMT+00:00
> > Subject: Re: Shutoff at Service Entrance
> >
> > Well for a real life situation where this exists, albeit in a very large
> > building in Kansas City --- picture a 1000 feet by 2000 feet building.
> > 10-inch fire mains running east-west and north-south through the building
> > with takeoffs for manifolded sprinkler systems of from 2-3 risers each,
> > typically.  The mains are looped and fed by fire pumps.  Lots of
> potential
> > for a super flood if you postulate the main breaking.   Leaks, unless
> > large, are not going to be picked up by a flow switch anyway.
> >
> > We also have the situation described where an underground lead-in enters
> > the building, goes up and overhead out to a manifold about a 100 feet
> into
> > the building - no valve at the outside wall, yard post valve, but there
> is
> > a drain at the low point at the exterior wall.
> >
> > It has been like this since 1942 and no major problems.  Yes pipe can
> leak
> > but 8 and 10-inch pipe won't rust through before the 6, 4, and smaller
> pipe
> > will.   Whether the code prohibits this or not, not sure how else you
> would
> > sprinkler a place like this.
> >
> > John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
> > Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
> > Security Administration's Kansas City Plant | Operated by Honeywell FM&T
> |
> > 2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
> > [email protected]
> >
> > ______________________________**_________________
> > Sprinklerforum mailing list
> > Sprinklerforum@firesprinkler.**org <[email protected]>
> > http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
> >
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <http://fireball.**firesprinkler.org/mailman/**
> > private/sprinklerforum/**attachments/20120913/e85ce981/**attachment.html<
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e85ce981/attachment.html
> >
> > >
> >
> > ______________________________**_________________
> > Sprinklerforum mailing list
> > Sprinklerforum@firesprinkler.**org <[email protected]>
> > http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/5564bca0/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------