Matt,

You have some "what ifs" in there,  "If any of the piping between the
flange and the riser was damaged, it would be a long time before the water
got shut off out at the pit... assuming the underground valve has been
properly maintained and still closes, and has not been buried or paved
over, and the pit is not full of water, etc...," and you know that will
always get me started, so... what if the aliens from V come and steal all
the water (unlikely), or the gate in the unnecessary extra valve drops
(relatively common), or the valve in the pit or the unnecessary valve is
closed and left that way (closed valves account for, if my memory serves me
well, 35% of all sprinkler failures), etc....? What ifs on the other side.
What if this didn't have the 100' of interior supply piping? Would you put
in an extra control valve for 20', or 10'? What's the cut-off line? What if
it had an extra 100' of UG? Would you put in an extra valve then? Because
it might take longer to shut off a valve because there might be damage (I
presume this is a large pipe running across a ceiling just like a main
would) does not seem to justify an extra multi-hundred dollar valve and the
added risk of an extra control valve (something statics demonstrate being a
real issue). Just my take on the whole thing.

On Thu, Sep 13, 2012 at 2:35 PM, Matt Grise <[email protected]> wrote:

> As far as I can tell, it is a bad idea, but not against code.
>
> I have a similar situation where the underground comes above grade just
> past the exterior wall, but then runs to a riser room at the interior of
> the building. We are putting a control valve at the flange right after the
> water enters.
>
> If any of the piping between the flange and the riser was damaged, it
> would be a long time before the water got shut off out at the pit...
> assuming the underground valve has been properly maintained and still
> closes, and has not been buried or paved over, and the pit is not full of
> water, etc...
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, September 13, 2012 4:27 PM
> To: [email protected]
> Subject: Re: Shutoff at Service Entrance
>
> Why care if all the sprinkler heads are beyond the point at which a
> notification means is installed. If I'm reading you correctly, somewhere
> between the water source for this pipe and where it enters the building
> there is a valve. After that valve the pipe enters the building, changes
> type to an aboveground type, and then continues across the building some
> 100'. At that point there is a riser of some sort with a waterflow
> detection device of some sort, and then the system (mains, cross-mains,
> branchlines, heads). If this is the case then there will be notification if
> any head opens, and since the detector's purpose is not to discover leaks,
> but rather sprinkler discharge, then why wouldn't this configuration be no
> different than if you had another 100' of UG before you even got to the
> building? Water purveyors and/or fire marshals may have rules as to what
> types of valves and where they must be located, and you may be subject to
> such local regulations, but there is nothing you've described as far as I
> can see that is prohibited in NFPA 13.
>
> On Thu, Sep 13, 2012 at 11:09 AM, Jarron Gass <[email protected]
> >wrote:
>
> > I should clarify that the piping is steel schedule 10, my issue is that
> > there is a significant distance between where it enters the building and
> > where the initial shut off valve is located.  There is a valve in a pit
> > outside, so it is possible to shut it down, but there is no flow switch
> on
> > this run of pipe to notify of water discharge.
> >
> > Thanks,
> >
> > Jarron
> >
> > Jarron J. Gass - J. & J. Fire Protection Co., Inc.
> > 101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151
> > emergency (724) 898-2481, [email protected], www.jandjfire.com
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > ParsleyConsulting
> > Sent: Thursday, September 13, 2012 10:29 AM
> > To: [email protected]
> > Subject: Re: Shutoff at Service Entrance
> >
> > To extend Roland's remarks, there is also language in the new edition of
> > -13 (and -24) which limits the length that underground pipe can be run
> > under
> > the foundation without arching, trenching or isolation valves to no more
> > than 10'-0" from the edge of the foundation.
> >
> > PARSLEY CONSULTING
> >
> > Ken Wagoner, SET
> >
> > 760.745.6181 voice
> >
> > 760.745.0537 fax
> >
> > [email protected] <mailto:[email protected]>e-mail
> >
> > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
> >
> >
> > On 9/13/2012 7:20 AM, Roland Huggins wrote:
> > > You will not find anything saying the use fo underground pipe above
> > > ground is NOT ok.  That's not how it works.  Underground pipe by
> > > definition and allowed use per Table 10.1.1 can only be used
> > > underground (as dictated by the title of the applicable sections and
> > > listing when required).  Allowed pipe material for above ground is
> > > defined by section 6.3.
> > >
> > > There is a new allowance in the 2013 edition that will make an
> > > exception for the stub-up to the system riser to be underground pipe.
> > >
> > > Roland
> > >
> > > On Sep 13, 2012, at 6:58 AM, Dick Culver wrote:
> > >
> > >>
> > >> I am struggling with whether it is allowable by NFPA13, 2007 edition
> > >> to have approximately 100' of "underground" piping inside the
> > >> building before the shutoff.  In this situation, there is a meter pit
> > >> outside of the building, then the UG enters the building and goes up
> > >> and across to the front of the facility and connects into the fire
> > >> sprinkler header.  There is no valve immediately where the piping
> > >> enters the building, or any means to monitor flow.  My understanding
> > >> is that this was a new UG to replace an old dilapidated one.  I have
> > >> not pinpointed anything in the code that tells me this is not ok,
> > >> however it just doesn't seem to be a good practice.  I appreciate any
> > >> guidance from anyone who might have dealt with a similar situation.
> > >>
> > >>
> > >>
> > >> ~Jarron
> > >>
> > >>
> > >
> > > -------------- next part -------------- An HTML attachment was
> > > scrubbed...
> > > URL:
> > > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> > > chments/20120913/71ab1b7a/attachment.html>
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/2f97fabf/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e44777e3/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to