Jarron,

You're monitoring waterflow of sprinklers. As long as the waterflow
detector is before all the sprinklers, after the sprinkler control valve
and before the first split in the system. You seem to have anywhere along
100' of pipe to locate the device. Unless there is a major savings in
conduit and wire that makes locating it away from the riser makes sense I'd
keep it at the riser since that's where we usually find them. There's
nothing along the 100' of pipe to monitor.

On Thu, Sep 13, 2012 at 4:57 PM, Jarron Gass <[email protected]> wrote:

> My concern is probably shifting more to whether or not this should have a
> flow switch for that portion of the piping.  I can accept that there is a
> shutoff outside in the meter pit, but i feel like this should be monitored.
>  That is probably more a want than a need.
>
> ~Jarron
>
> Sent from my Verizon Wireless Droid
>
> -----Original message-----
> From: [email protected]
> To: sprinklerforum@firesprinkler.**org <[email protected]>
> Sent: Thu, Sep 13, 2012 22:12:31 GMT+00:00
> Subject: Re: Shutoff at Service Entrance
>
> Well for a real life situation where this exists, albeit in a very large
> building in Kansas City --- picture a 1000 feet by 2000 feet building.
> 10-inch fire mains running east-west and north-south through the building
> with takeoffs for manifolded sprinkler systems of from 2-3 risers each,
> typically.  The mains are looped and fed by fire pumps.  Lots of potential
> for a super flood if you postulate the main breaking.   Leaks, unless
> large, are not going to be picked up by a flow switch anyway.
>
> We also have the situation described where an underground lead-in enters
> the building, goes up and overhead out to a manifold about a 100 feet into
> the building - no valve at the outside wall, yard post valve, but there is
> a drain at the low point at the exterior wall.
>
> It has been like this since 1942 and no major problems.  Yes pipe can leak
> but 8 and 10-inch pipe won't rust through before the 6, 4, and smaller pipe
> will.   Whether the code prohibits this or not, not sure how else you would
> sprinkler a place like this.
>
> John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
> Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
> Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
> 2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
> [email protected]
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://fireball.**firesprinkler.org/mailman/**
> private/sprinklerforum/**attachments/20120913/e85ce981/**attachment.html<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e85ce981/attachment.html>
> >
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/db50818a/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to