Well for a real life situation where this exists, albeit in a very large building in Kansas City --- picture a 1000 feet by 2000 feet building. 10-inch fire mains running east-west and north-south through the building with takeoffs for manifolded sprinkler systems of from 2-3 risers each, typically. The mains are looped and fed by fire pumps. Lots of potential for a super flood if you postulate the main breaking. Leaks, unless large, are not going to be picked up by a flow switch anyway.
We also have the situation described where an underground lead-in enters the building, goes up and overhead out to a manifold about a 100 feet into the building - no valve at the outside wall, yard post valve, but there is a drain at the low point at the exterior wall. It has been like this since 1942 and no major problems. Yes pipe can leak but 8 and 10-inch pipe won't rust through before the 6, 4, and smaller pipe will. Whether the code prohibits this or not, not sure how else you would sprinkler a place like this. John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security Administration's Kansas City Plant | Operated by Honeywell FM&T | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 | [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum