My concern is probably shifting more to whether or not this should have a flow switch for that portion of the piping. I can accept that there is a shutoff outside in the meter pit, but i feel like this should be monitored. That is probably more a want than a need.

~Jarron

Sent from my Verizon Wireless Droid

-----Original message-----
From: [email protected]
To: [email protected]
Sent: Thu, Sep 13, 2012 22:12:31 GMT+00:00
Subject: Re: Shutoff at Service Entrance

Well for a real life situation where this exists, albeit in a very large
building in Kansas City --- picture a 1000 feet by 2000 feet building.
10-inch fire mains running east-west and north-south through the building
with takeoffs for manifolded sprinkler systems of from 2-3 risers each,
typically.  The mains are looped and fed by fire pumps.  Lots of potential
for a super flood if you postulate the main breaking.   Leaks, unless
large, are not going to be picked up by a flow switch anyway.

We also have the situation described where an underground lead-in enters
the building, goes up and overhead out to a manifold about a 100 feet into
the building - no valve at the outside wall, yard post valve, but there is
a drain at the low point at the exterior wall.

It has been like this since 1942 and no major problems.  Yes pipe can leak
but 8 and 10-inch pipe won't rust through before the 6, 4, and smaller pipe
will.   Whether the code prohibits this or not, not sure how else you would
sprinkler a place like this.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120913/e85ce981/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to